#193792 04/20/10 01:50 AM
Joined: Mar 2005
Posts: 240
Member
how should I calculate generator feeders? I have a 17 KW generator 71 amps, 310.15 allows #4 for 100 amps, but does it allow #6 for 71 amps? Do I size according to 310.16 which is still #4?
Thanks,
H20

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
You can only use 310.15(B)(6) if this is a main feeder for the entire dwelling, basically an extension of the service entrance from a disconnect. That is, by definition, a #4 minimum. In no case could you interpolate down to a #6.
Any other application has to use 310.16.


Greg Fretwell
gfretwell #193802 04/20/10 12:46 PM
Joined: Mar 2005
Posts: 240
Member
thanks Gfretwell