A customer requests an addtional circuit (3 outlets) in a stand alone garage.
She has an outside 100 AMP disconnect at the entrance. From there the feeder goes direct to the oposite side of the house and terminates at a Ronk 100 AMP manual transfer switch (for a portable generator hookup).
EGC and all neutrals from the single house distribution panel and the stand alone garage distribution panel are bonded together inside the Ronk manual transfer switch. The house distribution panel and the stand alone garage distribution panel have egc and neutral seperate as required in each panel.
House panel is 125 AMP service. Stand alone garage panel is 100 AMP service.
I cannot find a code section on this. Q - Can both these two distribution panels be bonded together (EGC and neutral) at the same location inside the Ronk manual transfer switch? Q - If they can be does the 1st bond of neutral and ground at the outside service entrance disconnect (on the other side of the house) cause a problem by being a second EGC and neutral bond?
Thanks.
|
|
|
|
Joined: Jul 2004
Posts: 9,935 Likes: 34
Member
|
Short answer, no if the transfer equipment is not switching the neutral. You can only have one main bonding jumper in the system at a time.
Greg Fretwell
|
|
|
|
Joined: Apr 2010
Posts: 5
OP
New Member
|
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
well one can see the confusion in possibly having to add a GEC to the stand alone garage because it exceeds a single circuit here, and the specture of a SDS introduced.
In fact, many genny manufaturers provide a lug for a GEC to be made off it as well....
~S~
|
|
|
|
Joined: Jul 2004
Posts: 9,935 Likes: 34
Member
|
The real issue is not the ground electrode. It is the bonding jumper regrounding the neutral. As long as you keep the concept in mind that you can only have one bonding jumper in the system at any time and coordinate your transfer equipment and whether or not your generator is bonded you will be OK. The EGC system should always be connected together. It is the neutral that you switch or not.
Greg Fretwell
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
well said, an a very good general concept to keep in mind Greg
~S~
|
|
|
|
Joined: Jul 2004
Posts: 9,935 Likes: 34
Member
|
I didn't invent it. This was the way Jim Pauley on one of his road shows (a Soares pitch) explained it and it made perfect sense.
Greg Fretwell
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
Well Mr. Pauley saved himself lots of code-speak, reminds me of when i was told 'If it's metal, and doesn't move, bond it'
~S~
|
|
|
|
Joined: Apr 2010
Posts: 5
OP
New Member
|
Between Soars book on grounding and Mike Holts grounding and bonding book - which would you rather have in your library?
|
|
|
|
Joined: Jul 2004
Posts: 9,935 Likes: 34
Member
|
Why wouldn't you bond things that move? That's why they make braided bonding straps and stranded green wire Maybe I spent too much time on the load side of the plug cap. We bonded everything metal. Even a hinged cover got a bonding strap.
Greg Fretwell
|
|
|
Posts: 99
Joined: August 2003
|
|
|
|
|