First he would cut through a live piece of zip cord with a razor blade, protected by a standard 15 AMP breaker. There was a flash, breaker tripped and a small burn hole in the razor blade. Now the same test with a AFCI breaker, huge flash and the better part of the razor blade was missing. Needless to say I do not have a lot of confidence in these new breakers.
This is very interesting.
Did the factory rep mention anything about failure rates for these afcis, and why it would take so much longer to trip than a standard breaker.
I read somewhere that SQ-D QO breakers open in one cycle or 16.667 mili-seconds. and also that the AFCIs open in approx 8 cycles or 133 miliseconds. All things being equal this is still very fast. In real terms about 3 blinks of an eye.
When I first read about the afci technology the idea was that on 15 and 20 amp breakers there could be sustainable faults of less than 20 amps say 5, 10 15 amps, this was in the EC & M magizine, and these devices were to pick up these arching fault and open the breaker. Now that doesnt seem to be the case.
From what I have been reading is that there must be a sustainable 75 amp Arc for the app.8 cycles before the breaker will open up.
again all things being equal, it would take 6-10 times 20 to trip a standard breaker in less than a cycle.
So what are we looking at here a very selective devive ?
From what you describe the standard breaker opens faster than the afci under that kind of fault.
It doesnt sound like the factory rep had much faith in afci s.
What was his opinion ?
WOC