0 members (),
166
guests, and
8
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Jul 2004
Posts: 136
OP
Member
|
30KVA dry type transformer (480 X 120/208) Can it be located above a suspended accessible ceiling (say in a medical office building)? Can it be located above this ceiling if the ceiling space is a return air plenum?
|
|
|
|
Joined: Mar 2005
Posts: 212
Member
|
NEC 2008 450.13(B) says, generally for this size and type, you can. The plenum space question is not addressed.
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
300.22 (c)(2) should be read, and then I suggest you speak to the local AHJ for his/her interp. Under 50 KVA is no issue, BUT...the air handling ceiling needs to be addressed. Also, you may want to have a cut sheet for the exact xfr you intend to install.
John
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
I think this is probably legal, depending on the transformer but it might be a questionable design choice. If that transformer smokes it will share the joy with the rest of the building pretty fast, at least that HVAC zone anyway.
Greg Fretwell
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
If the Life Safety System ( Fire Alarm ) is up to snuff a duct detector is going to shut things down well enough in time.
Not quite the same set-up...
But I rigged a 45kVA XFRMR, dry-type, above a grid to give isolated power to data loads. Upon the detection of fire, within this space only, a shunt-trip killed total power - with a time delay of seconds so that the data state could be frozen/ preserved. Subsequently the dry fire system would be flooded into the now unpowered space.
So the question of plenum return air really would seem to be a life safety question not to be answered within our Code.
Tesla
|
|
|
Posts: 356