#193176 - 03/20/10 07:51 PM
Re: Intersystem grounding block
[Re: HotLine1]
|
Member
Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
|
John,
Above ceiling and wires on grid? OMG! that is a whole other subject. How many times have we gone into a building and found open boxes, open splices and old temp lighting above grid ceilings. Never mind the wires laying on the ceiling, there where all these open boxes, splices and wiring that was live and not protected.
As an AHJ, I demand an Above ceiling inspection, and I try to make sure that all of the old temp wiring is removed and all the boxes are closed up.
|
|
Top
|
|
|
|
#193182 - 03/20/10 08:05 PM
Re: Intersystem grounding block
[Re: HotLine1]
|
Member
Registered: 02/23/08
Posts: 167
Loc: Missouri
|
you drive a rod at a light pole and you dont connect it to the building grounds
|
|
Top
|
|
|
|
#193195 - 03/20/10 09:22 PM
Re: Intersystem grounding block
[Re: Rewire]
|
Member
Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
|
800.100 is an interesting read for these questions. Rewire, that rod on the pole is bonded to the service vis the grounded conductor.
_________________________
Greg Fretwell
|
|
Top
|
|
|
|
#193197 - 03/20/10 09:40 PM
Re: Intersystem grounding block
[Re: gfretwell]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Rewire:
A rod driven at a site light pole is bonded to the system via the EGC that is with the circuit conductors. Field procedure is Cadweld # 6 (or 4) to rod, tail up into pole base by feeders, bond to pole w/lug, tail pc. to splice to EGC. Design purpose of the rod at pole is lightning protection.
_________________________
John
|
|
Top
|
|
|
|
#193199 - 03/20/10 11:34 PM
Re: Intersystem grounding block
[Re: HotLine1]
|
Member
Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
|
I watched FPL replace a pole the other day and they didn't even use a rod. The #4 solid just runs to the bottom of the pole and gets a little coil on the bottom end of the pole. These are deep enough to be in the ground water so I imagine it is a decent electrode.
_________________________
Greg Fretwell
|
|
Top
|
|
|
|
#193203 - 03/21/10 09:02 AM
Re: Intersystem grounding block
[Re: gfretwell]
|
Member
Registered: 02/23/08
Posts: 167
Loc: Missouri
|
most of the light poles I have seen their is no piutail to the egc
|
|
Top
|
|
|
|
#193221 - 03/21/10 08:03 PM
Re: Intersystem grounding block
[Re: Rewire]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Time to clear the air.... The light poles that I reference herein are site lighting metal poles, installed by an EC, on private property. The 'rod' is a 'spec' item by the EE/PE/Arch.
I am not refering to utility poles (wood) installed and maintained by a utility here.
_________________________
John
|
|
Top
|
|
|
|
#193426 - 04/01/10 09:46 AM
Re: Intersystem grounding block
[Re: sparky]
|
Member
Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
|
I have seen blocks from both Arlington and Erico for this purpose. I assume both are UL listed.
|
|
Top
|
|
|
|
#193453 - 04/02/10 07:05 PM
Re: Intersystem grounding block
[Re: Jim M]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
JimM: IMHO, both brands you mention have UL listed bonding blocks; as to a specific model, can't tell ya.
_________________________
John
|
|
Top
|
|
|
|
#193643 - 04/12/10 07:36 AM
Re: Intersystem grounding block
[Re: HotLine1]
|
Member
Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
|
John,
OK there are UL listed and labeled Intersystem Grounding Blocks (IGB) but what if someone just used a left over ground terminal from a service panel. The "ground bar" is made out of copper. Would that pass an inspection?
|
|
Top
|
|
|
|
|