Any news on this issue?

I have a couple Qs:

1: Do _ALL_ the Lamps, controlled by the 3-Way loop, flicker when "Off"?

2: If #1 is "Yes", do they all flicker at the same rate, or flicker simultaneously?

3: After "Draining" the Lamps with the Resistive Load, does the 23V reappear, or do the Lamps begin flickering, once the Resistive Load is disconnected?

What may be experienced here is the discharging of Capacitors, or similar devices in the Ballast.

While this would be somewhat annoying to your Client, it should not be an operating issue, or otherwise cause a malfunction.

Suggestions by Members to shunt a Draining device, will be of benefit.
Either use an Incandescent Lamp in one Luminaire (if the fixtures have Screw-Shell Sockets), or connect a "Brute-Force" Drain - such as a Fixed Resistor, or Capacitor between L-N.
The Incandescent Lamp is the most safest and easiest method.

Keep us informed on the outcome.