The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
450.3(C)
by Tesla
05/23/12 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
05/23/12 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
Back to back bends on electric bender
by Tesla
05/20/12 05:38 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 17
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
1 registered (tbone), 122 Guests and 3 Spiders online.
Key: Admin, Global Mod, Mod
Page 4 of 4 < 1 2 3 4
Topic Options
Rate This Topic
#193146 - 03/19/10 09:56 PM Re: Transformer Secondary [Re: Scott35]
SJT Offline
Member

Registered: 07/24/02
Posts: 238
Loc: PATCHOGUE, N.Y.
Scott, Good drawings. Did you create those on Autocadd? Thanks

Top
#193162 - 03/20/10 01:05 PM Re: Transformer Secondary [Re: SJT]
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2562
Loc: Anaheim, CA. USA
SJT,

Yes, the drawings posted here at ECN were compiled within an AutoCAD Environment (drawn with AutoCAD).

BTW:
In regards to...
Quote:

I have to check the size of those Primary fuses, to make sure it's under that 125%.


Did you ever find out what size fuses were installed for Primary OCPD?

Let me know if there are any questions or comments.

Thanks for the reply. thanks beer

Scott
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#193283 - 03/24/10 09:13 PM Re: Transformer Secondary [Re: Scott35]
SJT Offline
Member

Registered: 07/24/02
Posts: 238
Loc: PATCHOGUE, N.Y.
I have not checked the Primary fuse size, but I will. The Bldg. is only 2 years old, and the original design should of had 3 circuits to the cubicle sections. there are 2 sections we will be running an additional circuit to each. Learned a few things about cubicle pre-fab modular wiring on this one. Think I'll open a Sam Adams cold one.