Transformers & Feeders:3P 4Wire Closed Delta
Five Drawings of Transformer Setups (Connection Schemes);
Primary and Secondary Feeders, Plus OCPDs and Panelboards for:
3 Phase 4 Wire Closed Delta Transformers
(Two Voltage SDS)
NOTE: Click on Image to view Full-Sized Image
---------------------------------------------------------
Drawing 3PH4W-CD1: 480V x 120/240V 3 Phase 4 Wire Closed Delta - Center Tap Grounded Neutral
(Max. Voltage To Ground = 200V, Nominal = 120V; With Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
---------------------------------------------------------
Drawing 3PH4W-CD2: 480V x 120/240V 3 Phase 4 Wire Closed Delta - Center Tap Grounded Neutral
(Max. Voltage To Ground = 200V, Nominal = 120V; With Grounded Conductor)
Single Panelboard fed by Secondary Feeders, Additional Panelboard "Subfed".
---------------------------------------------------------
Drawing 3PH4W-CD3: 480V x 120/240V 3 Phase 4 Wire Closed Delta - Center Tap Grounded Neutral
(Max. Voltage To Ground = 200V, Nominal = 120V;, With Grounded Conductor)
Two Panelboards fed via Tapped Feeder.
---------------------------------------------------------
Drawing 3PH4W-CD4: 480V x 120/240V 3 Phase 4 Wire Closed Delta - Center Tap Grounded Neutral
(Max. Voltage To Ground = 200V, Nominal = 120V; With Grounded Conductor)
Two separate Panelboards fed by Secondary Feeders- each set derived from "X" Terminals.
---------------------------------------------------------
Drawing 3PH4W-CD5: 480V x 120/240V 3 Phase 4 Wire Closed Delta - Center Tap Grounded Neutral
(Max. Voltage To Ground = 200V, Nominal = 120V; With Grounded Conductor)
Distribution Panel fed by Secondary Feeders.
-----------------------------------------------------------------------------------------
Text #3: Two Voltage SDS - Primary & Secondary OCPDs
(Click on Image to view Full-Sized Image)
-----------------------------------------------------------------------------------------