ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 235 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2000
Posts: 2,723
Likes: 1
Scott35 Online Happy OP
Broom Pusher and
Member
Transformers & Feeders: 3Ph 4Wire Open Delta

Five Drawings of Transformer Setups (Connection Schemes);
Primary and Secondary Feeders, Plus OCPDs and Panelboards for:
3 Phase 4 Wire Open Delta Transformers
(Two Voltage SDS)
NOTE: Click on Image to view Full-Sized Image

------------------------------------------------------------

Drawing 3PH4W-OD1: 480V x 120/240V 3 Phase 4 Wire Open Delta - Center Tap Grounded Neutral
(Max. Voltage To Ground = 200V, Nominal = 120V; With Grounded Conductor)
Single Panelboard fed by Secondary Feeders.
[Linked Image]

-----------------------------------------------------------

Drawing 3PH4W-OD2: 480V x 120/240V 3 Phase 4 Wire Open Delta - Center Tap Grounded Neutral
(Max. Voltage To Ground = 200V, Nominal = 120V; With Grounded Conductor)
Single Panelboard fed by Secondary Feeders, Additional Panelboard "Subfed".
[Linked Image]

-----------------------------------------------------------

Drawing 3PH4W-OD3: 480V x 120/240V 3 Phase 4 Wire Open Delta - Center Tap Grounded Neutral
(Max. Voltage To Ground = 200V, Nominal = 120V;, With Grounded Conductor)
Two Panelboards fed via Tapped Feeder.
[Linked Image]

-----------------------------------------------------------

Drawing 3PH4W-OD4: 480V x 120/240V 3 Phase 4 Wire Open Delta - Center Tap Grounded Neutral
(Max. Voltage To Ground = 200V, Nominal = 120V; With Grounded Conductor)
Two separate Panelboards fed by Secondary Feeders- each set derived from "X" Terminals.
[Linked Image]

-----------------------------------------------------------

Drawing 3PH4W-OD5: 480V x 120/240V 3 Phase 4 Wire Open Delta - Center Tap Grounded Neutral
(Max. Voltage To Ground = 200V, Nominal = 120V; With Grounded Conductor)
Distribution Panel fed by Secondary Feeders.
[Linked Image]

-----------------------------------------------------------------------------------------


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: Oct 2000
Posts: 2,723
Likes: 1
Scott35 Online Happy OP
Broom Pusher and
Member
Description Text for above images:

Text #3: Two Voltage SDS - Primary & Secondary OCPDs
(Click on Image to view Full-Sized Image)
[Linked Image]


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5