The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
100AMP panel in 60 degree ambient what size wire?
by sidmuer
05/23/12 09:25 AM
450.3(C)
by gfretwell
05/22/12 09:32 PM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
Back to back bends on electric bender
by Tesla
05/20/12 05:38 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 17
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
5 registered (gfretwell, EV607797, Webmaster, ameterguy, jdevlin), 123 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#193048 - 03/17/10 12:24 AM Ch9 table 1
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
Table one of Ch 9 says if we have one conductor we can fill the conduit to 53%, 2 conductor to 31% and more than 2 conductors the conduit can be filled to 40%.
My question is why 31% for 2 conductors and 40% for more than 2 conductors? what is rational behind it.

An IAEI instructor once told me it is because of the heat dissipation. But he did not explain in details why?

Thanks.
_________________________
Be kind to your neighbor, he knows where you live


Top
#193049 - 03/17/10 12:41 AM Re: Ch9 table 1 [Re: Niko]
gfretwell Online   content

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
It just has to do with how they pack into the pipe. Three takes up less room than 150% of 2 and it is volume we are speaking of.
Heat really doesn't enter into it. You derate "x" number of conductors the same no matter what size pipe it is in.
_________________________
Greg Fretwell

Top
#193053 - 03/17/10 08:14 AM Re: Ch9 table 1 [Re: gfretwell]
Rewire Offline
Member

Registered: 02/23/08
Posts: 167
Loc: Missouri
ask your instructor to elabroate.Then come tell us.

Top
#193057 - 03/17/10 02:44 PM Re: Ch9 table 1 [Re: Rewire]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
Rewire,
the instructor was at a seminar. so i don't have access to him anymore.

I have posted the same question at Mike's site http://forums.mikeholt.com/showthread.php?t=123904
but i am still not 100% confident on my understanding.
_________________________
Be kind to your neighbor, he knows where you live


Top
#193059 - 03/17/10 06:23 PM Re: Ch9 table 1 [Re: Niko]
Tesla Offline
Member

Registered: 06/16/04
Posts: 767
Loc: Sacramento, CA
It's the radius of the conductors...

Do the math.

It boils down to the straight geometry of circles.

The conduit/EMT is the big circle...

Now how many circles can you fit inside leaving enough room to pull in without excessive force/ruining the insulation.

That's all that's involved.
_________________________
Tesla

Top
#193061 - 03/17/10 07:26 PM Re: Ch9 table 1 [Re: Tesla]
Rewire Offline
Member

Registered: 02/23/08
Posts: 167
Loc: Missouri


Edited by Rewire (03/17/10 07:27 PM)

Top
#193076 - 03/18/10 11:44 AM Re: Ch9 table 1 [Re: Rewire]
sabrown Offline
Member

Registered: 12/12/02
Posts: 283
Loc: Ogden, Utah, USA
Expounding on Tesla, 3 conductors can line up in a straight line so all the diameters add up. 4 or more and bundle collapses (the conductors don't ever twist up to line out in a row. Thus the binding issue for 3 conductors.

Top
#193122 - 03/19/10 07:32 AM Re: Ch9 table 1 [Re: sabrown]
Rewire Offline
Member

Registered: 02/23/08
Posts: 167
Loc: Missouri
just when it all makes sense they bring in nipples

Top