The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
100AMP panel in 60 degree ambient what size wire?
by sidmuer
05/23/12 09:25 AM
450.3(C)
by gfretwell
05/22/12 09:32 PM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
Back to back bends on electric bender
by Tesla
05/20/12 05:38 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 17
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
5 registered (gfretwell, EV607797, Webmaster, ameterguy, jdevlin), 123 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#192884 - 03/08/10 06:15 PM Max distance of main panel from meter
twh Online   content
Member

Registered: 03/11/04
Posts: 607
Loc: Regina, Sask.
How far from where the service conduit enters a residential building can the panel be placed?

Top
#192885 - 03/08/10 06:27 PM Re: Max distance of main panel from meter [Re: twh]
wire twister Offline
Member

Registered: 11/25/06
Posts: 23
Loc: Washington GA USA
The AHJ in my area says "a reasonable distance" When pressed for a number he says a reasonable distance is 15 feet or less. Any further than that he requires disco/over current protection on the outside of the building. As far as a maxium with OCP he had no maximum.

Top
#192886 - 03/08/10 08:07 PM Re: Max distance of main panel from meter [Re: twh]
brsele Offline
Member

Registered: 07/29/08
Posts: 46
Loc: Georgetown, Ontario
Originally Posted By: twh
How far from where the service conduit enters a residential building can the panel be placed?


6-206 says: "As close as practical to the point where the consumer's service conductors enter the building."

What's the situation that you're looking at?

Bruce

Top
#192887 - 03/08/10 08:34 PM Re: Max distance of main panel from meter [Re: brsele]
dougwells Offline

Member

Registered: 05/03/03
Posts: 1126
Loc: kamloops BC Canada
we have had to bury teck and encase it in concrete to get around a chimmy on the out side to get to a panel location

Top
#192888 - 03/08/10 08:38 PM Re: Max distance of main panel from meter [Re: brsele]
twh Online   content
Member

Registered: 03/11/04
Posts: 607
Loc: Regina, Sask.
This is a Saskatchewan interpretation, from the SaskPower web site:
Quote:
6-206 (1)(e) Service Equipment:
As close as practicable shall not exceed 6 conduit meters. Where the service box or other consumer’s service equipment is located beyond 6 conduit meters from the point where the service conductors enter the building, the conductors shall be run in threaded rigid metal conduit for the entire length.
I like the definite rule, but wonder about the validity of an interpretation. At least they put it in writing.

The real situation is that a carpenter built a house and planned the meter location and panel location based on this rule. However, the panel could be in the basement bedroom and be closer to the meter. It could be practicable to have the panel in the bedroom.

So I put the panel in the furnace room, as far as 6m of conduit would reach. That seemed practicable in light of the interpretation.

I know I could phone the inspector, but I think I should be able to rely on my own judgement. I have a code book too. Anyway, I'm not sure that the inspector should be making the call and doing the inspection. It's too much like inspecting his own work.

What is the interpretation of practicable where you are?

Top
#192890 - 03/08/10 11:20 PM Re: Max distance of main panel from meter [Re: twh]
Navyguy Offline
Member

Registered: 10/14/05
Posts: 29
Loc: Welland, Ontario, Canada
On the exterior is can be as far as you want basically...once you enter the building this is what you get...

Originally Posted By: "OESC 24th Ed"
(1) Consumer’s service equipment location

Rule 6-206 requires that the service box or other consumer’s service equipment shall be as close as practicable to the point where the consumer’s service conductors enter the building.

Where judgment is required about “as close as practicable", the following may be used for guidance on the maximum length of run:

(a) 1.5 m into rooms or areas of combustible construction; or

(b) 7.5 m into other areas provided: the wiring method is rigid conduit, electrical metallic tubing (EMT) or a cable with a continuous metal sheath or interlocking armour and the conduit or cable is mechanically protected where it is within 2 m of the floor.


That is the Ontario perspective.

Cheers

Top
#192924 - 03/10/10 11:04 AM Re: Max distance of main panel from meter [Re: Navyguy]
mr_electrician Offline
Member

Registered: 06/22/07
Posts: 106
Loc: London, Ontario
I just built my own house and being an electrician I wired it as well. my load center is approx 25 feet from the meter base with no over current protection outside. How did it pass you may ask? Since my mechanical room is not on an exterior wall I ran my conduit through a sleve I put in the foundation (garage entrance side) and came up in the garage at the wall I needed to go through, then LB into mechanical room. My maximum conduit distance exposed is around 2.5 feet. Even though the service runs under my garage pad, it is not considered in the house yet.
PS. I used an expansion fitting before the conduit went underground. My conduit run was complete so I did not want settling dirt to rip my meter base off the wall!!! I also have about 200' of spare 3/4" conduit runs (6 runs) and 60' of 1" as well for future all stubed above the garage floor and through foundation below grade. Just in case!


Edited by mr_electrician (03/10/10 11:10 AM)
_________________________
Never trust an electrician with no eyebrows!!

Top
#192950 - 03/11/10 01:01 PM Re: Max distance of main panel from meter [Re: mr_electrician]
mikesh Offline
Member

Registered: 06/07/06
Posts: 567
Loc: Victoria, BC, Canada
In Victoria it is literal. As close as practicable. If I can find a legal location for a panel IE not a bathroom, coal bin, closet, crawlspace, and the contractor choses a place further into the building then it fails or gets encased in 2 inches of concrete. BC has a Directive on section 6 that expands on this but the absolute limit without concrete is 1.5 meter subject to that location being as close as practicable.

Top
#192957 - 03/11/10 06:16 PM Re: Max distance of main panel from meter [Re: mikesh]
twh Online   content
Member

Registered: 03/11/04
Posts: 607
Loc: Regina, Sask.
This is from a 2009 Standata from Alberta. I'm guessing it's their interpretation of reasonable:
Quote:
Rule 6-206 Consumer's Service Equipment Location: Length of Service Conductors in Buildings Rule 6-206(1)(e) requires that service equipment be located as close as practicable to the point where the service conductors enter the building. Rule 6-208 outlines where the conductors must be located. Both rules recognize that service conductors must enter the building to make connection to the service equipment. While it is generally agreed that in the interest of safety the unfused conductors within the building should be as short as possible, this distance is not clear. A recommended practice in Alberta is to limit the length of service conductor in the building to 3m. Where this is not practicable, service conductors may extend further inside the building provided they are mechanically protected in rigid metal conduit. The maximum distance for service conductors inside a building should not exceed 7.5 m.


I thought the rule about rigid conduit was an odd interpretation, but 2 inches of conduit is an even stranger interpretation of "as close as practicable".

Top
#192967 - 03/12/10 09:27 AM Re: Max distance of main panel from meter [Re: twh]
jdevlin Online   content
Member

Registered: 08/07/02
Posts: 355
Loc: welland ontario canada
It's 2 " of concrete not conduit. The concrete makes it fire safe since the conductors are not fused.

Top