The Electrical Contractor Network
ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals
Books, Tools and Test Equipment for Electrical and Construction Trades
Live Chat
Join in a Live Electrical Chat!
>> Enter/Register
  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Looking for a unique adjustment nut
by HotLine1
Today at 07:14 AM
A taper or B taper, which is it?
by JoeTestingEngr
Today at 12:39 AM
GE low-voltage remote control relay system
by Albert
Yesterday at 10:26 PM
Electrical systems in mobile structures.
by gfretwell
Yesterday at 09:21 PM
Conduit Bending Apps for iPhone -Master Bender
by KJay
Yesterday at 08:31 PM
A What's right here??
Shout Box
Top Posters (30 Days)
gfretwell 72
HotLine1 68
KJay 34
sparky 28
renosteinke 26
Classified Ads:
Electrical-Classifieds.com
Who's Online
1 registered (Albert), 119 Guests and 2 Spiders online.
Page 2 of 2 < 1 2
Topic Options
Rate This Topic
#192346 - 02/09/10 08:54 AM Re: GFCI breaker vs recepticle for 210.8a [Re: sparky]
ghost307 Offline
Loc: Chicago Illinois USA
Nope.
The electronics sense a difference in current between the outgoing and returning conductors. As long as none of those sneaky little electrons find a way to leave the wire partway through the circuit, there will be no overall effect.
_________________________
Ghost307
Top
#192348 - 02/09/10 11:46 AM Re: GFCI breaker vs recepticle for 210.8a [Re: ghost307]
gfretwell Offline
Loc: Estero,Fl,usa
I have heard there is a maximum amount of connected wire you can have because of capacitive coupling but so far I haven''t seen that and I have some pretty long GFCI runs. The longest is THHN in EMT which is supposed to be a worst case scenario.
Top
#192363 - 02/10/10 10:10 AM Re: GFCI breaker vs recepticle for 210.8a [Re: gfretwell]
sabrown Offline
Loc: Ogden, Utah, USA
Greg, I am not sure that capacitive coupling is what you mean. In the case of extremely long runs of THHN there will be current leakage through the insulation of the wire to the ground which could add up to trip a GFCI. This can be mitigatted by going to a better insulation type like XHHW. But given enough length even it won't work. This really dosen't matter to much though because we have exceeded even the usual operation lengths of the circuit (volatage drop and it is better to place another panel to shorten the lengths of runs). I have not bothered to calculate what those lengths may be, if I had time I would. I just all stems from electricity takes all paths and even insulation is a path, just a mighty poor one.
Top
#192386 - 02/11/10 12:19 PM Re: GFCI breaker vs recepticle for 210.8a [Re: sabrown]
SteveFehr Offline
Loc: Chesapeake, VA
Receptacles are cheaper and often far more convenient. There's little reason to go with a GFCI breaker unless it's a situation where a GFCI receptacle just isn't a practical solution.
As to trips... Mine trip routinely, when I leave extension cords on the ground in the rain.
Top
#192394 - 02/11/10 03:42 PM Re: GFCI breaker vs recepticle for 210.8a [Re: SteveFehr]
sparky Offline
hmm, well i never really liked the idea of gfci's anywhere near the weather. Maybe i've seen a little too much abuse, incidents where the line side could be compromised, missing covers, etc.
Usually, i'll start a 'rough out' with a service gfci under , or near the panel. I'll make single runs back to that gfci to all the non-dedicated gfci's. That way they can be parsed out into dedicated circuits in the future.
That's paid off a number of times for me on those 'don't know what i'm building 'til i get there'jobs i've had the good fortune to step into...
~S~