The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
4" PVC Conduit For Sale - Chicago
by acastillo
05/23/12 01:12 PM
4" PVC Conduit For Sale In Chicago
by acastillo
05/23/12 01:12 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
05/23/12 09:25 AM
450.3(C)
by gfretwell
05/22/12 09:32 PM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 17
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
4 registered (jdevlin, sidmuer, twh, ampherder), 126 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Page 2 of 2 < 1 2
Topic Options
Rate This Topic
#192346 - 02/09/10 08:54 AM Re: GFCI breaker vs recepticle for 210.8a [Re: sparky]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 649
Loc: Chicago Illinois USA
Nope.

The electronics sense a difference in current between the outgoing and returning conductors. As long as none of those sneaky little electrons find a way to leave the wire partway through the circuit, there will be no overall effect.
_________________________
Ghost307

Top
#192348 - 02/09/10 11:46 AM Re: GFCI breaker vs recepticle for 210.8a [Re: ghost307]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
I have heard there is a maximum amount of connected wire you can have because of capacitive coupling but so far I haven''t seen that and I have some pretty long GFCI runs. The longest is THHN in EMT which is supposed to be a worst case scenario.
_________________________
Greg Fretwell

Top
#192363 - 02/10/10 10:10 AM Re: GFCI breaker vs recepticle for 210.8a [Re: gfretwell]
sabrown Offline
Member

Registered: 12/12/02
Posts: 283
Loc: Ogden, Utah, USA
Greg, I am not sure that capacitive coupling is what you mean. In the case of extremely long runs of THHN there will be current leakage through the insulation of the wire to the ground which could add up to trip a GFCI. This can be mitigatted by going to a better insulation type like XHHW. But given enough length even it won't work. This really dosen't matter to much though because we have exceeded even the usual operation lengths of the circuit (volatage drop and it is better to place another panel to shorten the lengths of runs). I have not bothered to calculate what those lengths may be, if I had time I would. I just all stems from electricity takes all paths and even insulation is a path, just a mighty poor one.

Top
#192386 - 02/11/10 12:19 PM Re: GFCI breaker vs recepticle for 210.8a [Re: sabrown]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Receptacles are cheaper and often far more convenient. There's little reason to go with a GFCI breaker unless it's a situation where a GFCI receptacle just isn't a practical solution.

As to trips... Mine trip routinely, when I leave extension cords on the ground in the rain.

Top
#192394 - 02/11/10 03:42 PM Re: GFCI breaker vs recepticle for 210.8a [Re: SteveFehr]
sparky Offline
Member

Registered: 10/18/00
Posts: 5433
hmm, well i never really liked the idea of gfci's anywhere near the weather. Maybe i've seen a little too much abuse, incidents where the line side could be compromised, missing covers, etc.

Usually, i'll start a 'rough out' with a service gfci under , or near the panel. I'll make single runs back to that gfci to all the non-dedicated gfci's. That way they can be parsed out into dedicated circuits in the future.

That's paid off a number of times for me on those 'don't know what i'm building 'til i get there'jobs i've had the good fortune to step into...

~S~

Top