The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
Looking for a unique adjustment nut
by HotLine1
Today at 07:14 AM
A taper or B taper, which is it?
by JoeTestingEngr
Today at 12:39 AM
GE low-voltage remote control relay system
by Albert
Yesterday at 10:26 PM
Electrical systems in mobile structures.
by gfretwell
Yesterday at 09:21 PM
Conduit Bending Apps for iPhone -Master Bender
by KJay
Yesterday at 08:31 PM
New in the Gallery:
A What's right here??
Shout Box

Top Posters (30 Days)
gfretwell 72
HotLine1 68
KJay 34
sparky 28
renosteinke 26
Classified Ads:


Electrical-Classifieds.com

Who's Online
1 registered (Albert), 119 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#192333 - 02/08/10 03:42 PM Old work grounding stumper
Haligan Offline
Member

Registered: 02/25/04
Posts: 109
Loc: Berkeley, CA USA
The Scene:
Old work bathroom remodel. GC has it down to the studs.
I'm keeping the existing circuit for lights and fan. 12/2 NM, no grounding
I've pulled a homerun 20a for receps.

How to ground the lights and fan?
A. There's a bare 14ga conductor that was bonding all of the old metal boxes. It is clamped with a grounding electrode to the bathroom's water pipe. This wire then continues off to other parts of the house. I could tap into this. But! Code says bonding to water pipe has to be 5' from source. This seems like a 'better than nothing' option. My least favorite so far.

B. Connect to the grounding of the new 20a circuit. This goes back to the panel and straight to the rod. Problem- I scoured the code and couldn't find an allowance for this.

C. Connect a new electrode and ground the lights and fan to the water pipe.

D. Run 12ga grounding wire all the way back to the panel. This is okay code wise, but raises some new issues.

What's best here?

Top
#192334 - 02/08/10 05:52 PM Re: Old work grounding stumper [Re: Haligan]
Jim M Offline
Member

Registered: 08/10/01
Posts: 451
Loc: Chestertown, MD, USA
Since you are down to the studs I would think that a new lighting circuit should be run.

Top
#192336 - 02/08/10 06:26 PM Re: Old work grounding stumper [Re: Jim M]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4766
Loc: Brick, NJ USA
I tend to agree with Jim M.
You may want to run your list of options past the local AHJ, as he is the one to accept or reject your choice(s).
_________________________
John

Top
#192337 - 02/08/10 07:51 PM Re: Old work grounding stumper [Re: HotLine1]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7034
Loc: Estero,Fl,usa
Best practice would be to run a new wire. Your ideas of using the water pipe, even with another rod, won't work unless you bond back to the existing ground electrode system.
You could share the EGC of the new receptacle circuit you have run but you do have to worry about protecting the wire you run. I would ask if your AHJ is OK with just stringing a THHN over to the receptacle box

Quote:
250.120(C) Equipment Grounding Conductors Smaller Than 6 AWG. Equipment grounding conductors smaller than 6 AWG shall be protected from physical damage by a raceway or cable armor except where run in hollow spaces of walls or partitions, where not subject to physical damage, or where protected from physical damage.
_________________________
Greg Fretwell

Top
#192338 - 02/08/10 08:58 PM Re: Old work grounding stumper [Re: gfretwell]
George Little Offline
Member

Registered: 01/18/04
Posts: 1437
Loc: Michigan USA
Guess I'm trying to figure out why anything has to be done with existing. But if you insist on doing something, item D. is the only one that meets code.
_________________________
George Little

Top
#192339 - 02/08/10 09:34 PM Re: Old work grounding stumper [Re: George Little]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7034
Loc: Estero,Fl,usa
I was just trying to let safety trump a technical violation (extending the EGC from an existing circuit of sufficient size). I would rather have a ground than not.
_________________________
Greg Fretwell

Top
#192340 - 02/08/10 10:38 PM Re: Old work grounding stumper [Re: gfretwell]
George Little Offline
Member

Registered: 01/18/04
Posts: 1437
Loc: Michigan USA
I guess I agree with you Greg and I would add, another option would be to wire the fan and lights in the bathroom on the new receptacle circuit. As long as he didn't extend to anything beyond the one bathroom, he'd have not only grounding but GFCI protection ta boot.
_________________________
George Little

Top
#192341 - 02/08/10 11:36 PM Re: Old work grounding stumper [Re: George Little]
Haligan Offline
Member

Registered: 02/25/04
Posts: 109
Loc: Berkeley, CA USA
George- I'm liking 210.11(C)3. The lights and the fan sum up to less than 1amp. Plenty of leftover on the 20a dedicated.

Thanks all

Top
#192345 - 02/09/10 08:29 AM Re: Old work grounding stumper [Re: George Little]
Rewire Offline
Member

Registered: 02/23/08
Posts: 167
Loc: Missouri
Originally Posted By: George Little
Guess I'm trying to figure out why anything has to be done with existing. But if you insist on doing something, item D. is the only one that meets code.
The only method that would be questionable would be B but all the others are code compliant