The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
4" PVC Conduit For Sale - Chicago
by acastillo
44 minutes 12 seconds ago
4" PVC Conduit For Sale In Chicago
by acastillo
44 minutes 54 seconds ago
100AMP panel in 60 degree ambient what size wire?
by sidmuer
Today at 09:25 AM
450.3(C)
by gfretwell
Yesterday at 09:32 PM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 17
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
4 registered (jdevlin, sidmuer, twh, ampherder), 129 Guests and 3 Spiders online.
Key: Admin, Global Mod, Mod
Page 2 of 3 < 1 2 3 >
Topic Options
Rate This Topic
#189747 - 10/23/09 01:48 PM Re: Plan Check requirements and "preferences" [Re: Scott35]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
I find it strange that any CAD program would screw up the receptacle placement on resi.
I have an ancient Windoze 3 version of 3D Architect that has always placed receptacles that meet 210.52(A). I never played with the "kitchen" on it so I am not sure if it is 210.52(B) aware.
It was interesting that Lee County took the plans I printed off of 3D architect for my addition (after the engineer stamped them) after 3 passes at plan review from his CAD program.
They may have just been tired of seeing me there tho.

My electrical plan went through on the first pass. wink
_________________________
Greg Fretwell

Top
#189748 - 10/23/09 03:40 PM Re: Plan Check requirements and "preferences" [Re: gfretwell]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Greg:
It's not so much that the CAD programs have an issue; it's more like the info isn't requested of the program(s)
_________________________
John

Top
#190337 - 11/11/09 06:25 PM Re: Plan Check requirements and "preferences" [Re: HotLine1]
luckyshadow Offline
Member

Registered: 01/04/05
Posts: 302
Loc: Maryland USA
We see an issue with emergency panels and what can be in them. There seems to be a problem with folks grasping Legally required, optional, and emergency systems ( art. 700,701 & 702). Commercial Kitchen GFCI protected outlets get missed on the drawings alot, Patient care areas of medical offices is another missed item on the drawings.

I'm amazed at the drawings that come for review and the one line diagrams don't match the equipment drawn. (One line shows a 200 ampere panelboard and the drawings call for a 150)

Top
#191595 - 01/03/10 06:11 PM Re: Plan Check requirements and "preferences" [Re: Scott35]
RH1 Offline
Member

Registered: 08/18/09
Posts: 22
Loc: California
My biggest problem with Architects is when they foolishly try to impress me with their poor grasp of electrical code. Please Mr. Architect, I know which receptacles need to be GFI protected. I laughed out loud in an Architect's face last year when every fixture was called a "Luminairie". Recently I've noticed a trend of calling the Master Bedroom the "Master's Bedroom". This is creepy on many levels.

I have made a career out of wiring high end custom homes and and the caliber of Architects in this industry is appalling. These near-do-wells have just recently discovered AFCI circuits and now they must call out every AFCI outlet in the house, it's so annoying, they are so convinced their code knowledge is superior to mine, I never miss an opportunity to embarrass one in front of the customer.

I was walking a job with one I call "Little Lord Faultleroy", a polished dandy with a brain as small as his bank account is large. He wanted Halo fluorescent cans with 100 watt lamps. Even had it on the plans. I informed this well coiffed clod that there was no such thing. He said he knew more about lighting than I did and that he would produce a catalog cut for me. I wound up installing 26 watt lamps, he never responded to request for the cuts...

I have never, in 30 years in construction, met an Architect that was not a poser or an outright impostor.



Edited by RH1 (01/03/10 06:12 PM)

Top
#191687 - 01/07/10 01:53 PM Re: Plan Check requirements and "preferences" [Re: RH1]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 649
Loc: Chicago Illinois USA
I worked with 1 Architect who absolutely floored me.

He asked if my Electric Closet was large enough, he went out of his way to stack them so I had a riser shaft, he pitched a fit when the other trades tried to run pipes through the room...so I asked the obvious question.

He had put himself through Architectural school with money that he made working construction for an Electrical Contractor between semesters.

He was the first (and so far the only) guy in that business I ever met who had a friggin' clue what we go through every day.
_________________________
Ghost307

Top
#191688 - 01/07/10 05:51 PM Re: Plan Check requirements and "preferences" [Re: ghost307]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
A quick comment on a job in review now (still)
Plans sealed by Arch & signed; 4th or 5th rev of E pages, one of which arrived today. Load calcs in panel schedule have math errors (addition). 225 amp fuses in 200 amp disco; 4x4/0 in 1-1/2" 'condit'....etc., etc.
_________________________
John

Top
#192061 - 01/25/10 07:53 AM Re: Plan Check requirements and "preferences" [Re: HotLine1]
harold endean Offline
Member

Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
John,


Do you ever get a good plan on the grounding, especially isolated grounding systems? I had several plans for schools which didn't even show anything about the ground system.

Top
#192069 - 01/25/10 12:49 PM Re: Plan Check requirements and "preferences" [Re: harold endean]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
harold:
Yes, on occasion a really good (overboard) grounding (oops earthing) plan comes in.

Basically, IF 250 is not addressed on comm plans, it gets a reject letter. Most of the EE/PE/Arch include 250 items on the plans, and a lot of 'boiler plate' spec within the notes.

BTW, I just opened responses to a Nov. '09 rejection that is resubmitted, and it is going back to the reject pile, along with the appropriate letters.
_________________________
John

Top
#192103 - 01/27/10 07:37 AM Re: Plan Check requirements and "preferences" [Re: HotLine1]
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2562
Loc: Anaheim, CA. USA
Everyone;
Thanks so much for contributing to this discussion! We are getting some applicable topics to discuss, along with some "Good - vs - Bad" Plan submissions.

I would like to post a recently completed Plan Set for your review and opinions. Plan Sheets will be PDFs, with a link to the files (uploaded to my website).
First I need to mask or remove the Client's information, and the Building Department information too.

This Electrical Design-Build Project is a good example of a complex Electrical System, within an older, existing Light Industrial Building.

The most satisfying elements of this particular Project have been:

1: Received compliments from the Plans Examiner (Examiner was very appreciative of contents),

2: Inspections went very smoothly (ease of coordination between Plans -vs- Field Conditions, panel labeling + directories coordinate with Plans, aux. documents available for review),

3: Client is extremely satisfied with complete Design-Build, and has suggested our Services to others,

4: Project was profitable.

The Project was an Industrial T.I. within an existing 12,800 sq. ft. Concrete Tilt-Up, built in 1956.

Existing to remain Services (2):
a: 400 Amp; 120/240V 1Ø 3W "Lighting" Service - with KWH Meter,

b: 400 Amp; 240V 3Ø 3W "Power" Service - with KWH Meter...
(both Services derived from a single 4 wire Delta Pole mounted Transformer setup - supplied by the local Utility).

Client equipment includes:
a: (2) 40 HP Air Compressors, with 460V 3 Phase Squirrel Cage Motors (both run coincidentally > 3 Hours per day, 6 days a week),

b: (2) Sand Blast Booths, with 7.5 HP 230V 3 Phase Dust Collection Motors (both used coincidentally, > 3 Hours per day, 6 days a week),

c: (2) Gas Ovens with 5 HP 230V 3 Phase Blower Motors (both used coincidentally, > 3 Hours per day, 6 days a week),

d: (1) Paint Spray Booth, with 7.5 HP 230V 3 Phase Motor (used > 3 Hours per day, 6 days a week),

e: (4) 30 Amp, 120V "Warmers" - for fabrics and PVC setting (used >3 Hours per day, 6 days a week),

f: (1) 5 HP, 230V 3 Phase Banding Machine (used 15 min. per Hour, 6 days a week),

g: Misc. 120V < 20 Amp loads (intermittent, 6 days a week).

Design included a new 480V SDS for the Air Compressors:
240V Delta Primary x 480V 3 Phase 3 Wire Corner Grounded Delta Secondary (Phase "B" = Grounded Conductor).

Client builds and repairs Indoor & Outdoor Metallic Furniture - of medium to large sizes. Staff is active 6 days per week, 7.5 Hours per day (1/2 hr lunch). Equipment is in use up to 85% of the day, Monday through Saturday (excluding Holiday periods).

Will post link as soon as possible.
Looking for any and all comments + critique.

Scott
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#192109 - 01/27/10 01:41 PM Re: Plan Check requirements and "preferences" [Re: Scott35]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Scott:
Based on the above...
1: Congrats on the success.
2: I would be a happy guy IF I got info that you listed in the above post, as opposed to...3 exhaust fans?? and two rooftop HVAC units!
_________________________
John

Top