#192266 - 02/03/10 08:45 PM High Voltage on the Ground
electure Online   sleepy

Moderator
Member

Registered: 12/24/00
Posts: 3971
Loc: Fullerton, CA USA


Submitted by: Harold Endean


Quote:

The power company here had an underground service go bad, so they temporarily ran wires to the factory.
Now that wouldn't be so bad, but these are primary wires, 3 lines and they are running on the ground alongside of a road.
They also cross the road twice. You can see where the wire runs down from the pole, across the road, along the road, over a fence, cross another driveway.
I believe each wire is about 7KV and there are 3 lines.

Pretty scary ain't it!


Harold


















Top
#192267 - 02/03/10 08:50 PM High Voltage on the Ground [Re: electure]
electure Online   sleepy

Moderator
Member

Registered: 12/24/00
Posts: 3971
Loc: Fullerton, CA USA










Top
#192272 - 02/04/10 08:36 AM Re: High Voltage on the Ground [Re: electure]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 647
Loc: Chicago Illinois USA
I especially like the way that they hop the fence.
I sure hope that they told the lawn service not to mow that day.
_________________________
Ghost307

Top
#192276 - 02/04/10 05:50 PM Re: High Voltage on the Ground [Re: ghost307]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4766
Loc: Brick, NJ USA
Harold:
Thanks for the pics!

If you want to add any comments....please do.

Which POCO? "FE" on the cone don't say much to me. I've never seen a 'temp' like that anywhere.
_________________________
John

Top
#192277 - 02/04/10 07:22 PM Re: High Voltage on the Ground [Re: HotLine1]
JoeKP Offline
Member

Registered: 03/29/08
Posts: 127
Loc: Berkley, MA
that's just horrible, id like to see the plows come through with the snow...
_________________________
-Joe
“then we'll glue em' then screw em'”
-Tom Silva
TOH

Top
#192278 - 02/04/10 09:21 PM Re: High Voltage on the Ground [Re: JoeKP]
noderaser Offline
Member

Registered: 03/01/07
Posts: 401
Loc: Portland, Oregon, United State...
Even though the insulation is pretty tough, it looks like a liability nightmare. What did the temp feed, that was so important to get power in right away? Big $$$ customer, or life & safety?
_________________________
http://www.hsiprodsvcs.com/

Top
#192296 - 02/05/10 10:00 PM Re: High Voltage on the Ground [Re: noderaser]
BigJohn Offline
Member

Registered: 03/06/04
Posts: 352
Loc: Boston, MA
That's pretty ridiculous.

Even when out transmission utility has open lines like that inside fenced substations they still mark and guard the heck out of them. What would've been wrong with stringing the length of that with "danger" signs of some sort? Warning ribbon isn't that expensive.

I especially like the totally unprotected lines in the road between the cones and the cover plate. That stuff is tough, but trucks are awfully heavy....

-John

Top
#192297 - 02/05/10 11:35 PM Re: High Voltage on the Ground [Re: BigJohn]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 932
Loc: Wi/ Paris France { France for ...
I do recall seeing that type of cable and I did used on 14 KV system without issue however laying top of the ground now that is tempting for trouble especaly if this cable is non conrated netural cable { most will have copper or steel wire warp around the cable }

But once hevey truck hit it it don't take much to get it have heckva a big flashover .,,, crazy

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#192312 - 02/06/10 01:00 PM Re: High Voltage on the Ground [Re: frenchelectrican]
mbhydro Offline
Member

Registered: 02/21/03
Posts: 228
Loc: Winnipeg MB Canada
I have seen this once when the telco lost the u/g to the exchange that served my part of the city due to a water main break.

The temp feed was covered for two days with planking and barricades / warning tape for the couple hundred feet from the drop pole to the transformer.

This was over a city sidewalk and lawn so truck damage was not an issue.

Top
#192315 - 02/06/10 05:55 PM Re: High Voltage on the Ground [Re: mbhydro]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8339
Loc: SI,New Zealand
Man,
That is just slack IMO.
I can't help but feel, that some sort of temporary poles could have been sunk for this circuit, to get it up out of the way.
I mean, that is what electricity utilities do as their bread and butter isn't it?
I just shook my head when I saw them wires laid over the top of that fence, it would have taken a few seconds to run them singles UNDER the fence.
It's like someone just doesn't care. bash
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#192377 - 02/11/10 05:24 AM Re: High Voltage on the Ground [Re: Trumpy]
RODALCO Offline
Member

Registered: 12/08/05
Posts: 850
Loc: Titirangi, Akld, New Zealand
That is a rough job.
I'm amazed that the POCO get's away with that.
Partially uncovered cables at a road crossing, hardly any warning signs and across that fence.
How long did they keep that going for ?
_________________________
The product of rotation, excitation and flux produces electricty.

Top
#192593 - 02/18/10 08:45 PM Re: High Voltage on the Ground [Re: Trumpy]
gpsparky Offline
Member

Registered: 03/30/08
Posts: 27
Loc: Kansas
Hope nobody tries to steal those cables, what with the price of copper these days...
_________________________
Sometimes not getting what you want can be an incredible stroke of luck.

Top
#192600 - 02/19/10 12:31 AM Re: High Voltage on the Ground [Re: gpsparky]
noderaser Offline
Member

Registered: 03/01/07
Posts: 401
Loc: Portland, Oregon, United State...
I'm assuming they are probably aluminum? Would be a pretty good steal if they were copper, assuming you got past the HV "security" system.
_________________________
http://www.hsiprodsvcs.com/

Top
#192605 - 02/19/10 08:17 AM Re: High Voltage on the Ground [Re: noderaser]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 647
Loc: Chicago Illinois USA
At 60Hz, the voltage in each cable goes to zero 120 times per second.

You can steal the wires while energized, but you need to have perfect timing and be really, really, really quick.

smile
_________________________
Ghost307

Top
#192633 - 02/20/10 12:41 PM Re: High Voltage on the Ground [Re: Trumpy]
harold endean Offline
Member

Registered: 02/16/02
Posts: 1813
Loc: Boonton, NJ
John,

The PoCo is the one in northern NJ. This all came about ( I found out) due to overtime. The factory didn't want to be without power during the day and the PoCo didn't want to pay the OT to their guys to work at night. SO, they just left the wire on the ground. The administrator in my town got on the phone with the PoCo and gave them holy hell. However it still took 2 weeks to resolve the issue. In that 2 weeks, kids and dogs played in the area and the town trucks plowed the snow.

Top
#192634 - 02/20/10 12:43 PM Re: High Voltage on the Ground [Re: harold endean]
harold endean Offline
Member

Registered: 02/16/02
Posts: 1813
Loc: Boonton, NJ
Did anyone see the e-mail going around called Dallas copper thieves? That shows you what happens when you try to steal HV wires while they were on.

Top
#192651 - 02/21/10 04:54 AM Re: High Voltage on the Ground [Re: harold endean]
SimonUK Offline
Member

Registered: 10/15/04
Posts: 50
Loc: Ayrshire, Scotland, UK.
A man was badly burned here about 6 months ago trying to steal copper cable. think the report said 11kv.

Top
#194434 - 06/02/10 01:37 AM Re: High Voltage on the Ground [Re: Trumpy]
lukemon2 Offline
Member

Registered: 08/23/06
Posts: 26
Loc: Petal, MS, USA
Holy Crap
_________________________
Luke McCoy The NEC Crazy Boy

Top
#194547 - 06/09/10 08:28 PM Re: High Voltage on the Ground [Re: harold endean]
mxslick Offline
Member

Registered: 10/24/04
Posts: 773
Loc: Hawthorne, CA USA
Originally Posted By: harold endean
Did anyone see the e-mail going around called Dallas copper thieves? That shows you what happens when you try to steal HV wires while they were on.


Yep I got that email..it was extremely graphic but proved the point of how dangerous the theft practice is.

As for what the OP posted..heads would roll if our local POCO tried that stunt. Our county code enforcement officials are ruthless here.

There was absolutely no excuse for the half-butt work shown in those pics.
_________________________
Stupid should be painful.

Top
#194569 - 06/11/10 08:03 AM Re: High Voltage on the Ground [Re: mxslick]
harold endean Offline
Member

Registered: 02/16/02
Posts: 1813
Loc: Boonton, NJ
MX,

Luckily that mess was only on the ground for a week, which is 6 days and 23 hours too long! However nobody got hurt. This also happened in the last winter and the town was still plowing roads. Imagine if there was a snow fall and the road dept. didn't see that wire laying on the road! Ouch!

Top
#194806 - 06/23/10 02:20 AM Re: High Voltage on the Ground [Re: harold endean]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 831
Loc: Alaska
some how "wow!" does not cover it.
_________________________
"Good judgment comes from experience. Experience comes from bad judgment."

Top
#197659 - 12/13/10 08:19 AM Re: High Voltage on the Ground [Re: sparkyinak]
harold endean Offline
Member

Registered: 02/16/02
Posts: 1813
Loc: Boonton, NJ
Should this fit the category, "What is the hookiest thing I ever saw hooked up" NAW! It is the scariest!

Top
#197674 - 12/13/10 06:06 PM Re: High Voltage on the Ground [Re: harold endean]
sparky Offline
Member

Registered: 10/18/00
Posts: 5433
harold

in the realm of 'scariest', 'just plain wrong', or maybe 'raise those little neck hairs' you win , hands down

~S~

Top
#197679 - 12/13/10 07:22 PM Re: High Voltage on the Ground [Re: sparky]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4766
Loc: Brick, NJ USA
~s~:

Harold and I are in the same state, he's up in the northwest area, and that may have been the same POCO, but I have to say, I have never seen anything even close to that.
_________________________
John

Top
#197701 - 12/15/10 08:53 AM Re: High Voltage on the Ground [Re: HotLine1]
harold endean Offline
Member

Registered: 02/16/02
Posts: 1813
Loc: Boonton, NJ
John,

The POCO here that did this fiasco starts with the first letter of your first name! smile

Top
#197703 - 12/15/10 08:54 AM Re: High Voltage on the Ground [Re: harold endean]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4766
Loc: Brick, NJ USA
Harold:
OK, I have them home, but not in my work township.
_________________________
John

Top