1 members (Scott35),
176
guests, and
10
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
OP
Member
|
When doing an Residential service upgrade and the GEC to the Water main is replaced, what do you do with the old one? Leave it connected or cut it out? Please include your reasoning. Bill
Bill
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
ok i'll play! if it is truely an 'upgrade' then the GEC required is probably larger, the old clamps are probably rusted, etc.] usually i find the old connections NG due to corrosion, and replace with new geased ( no-lox) clamps. The older ones usually do not 'jump' the meter, so in that sense they are NG also. so why leave the old one anyhow? i don't get it? am i slow here? hey,if you were dropped on your head as a baby would it be your fault??? [This message has been edited by Webmaster (edited 06-07-2001).]
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
OP
Member
|
Sparky, (Serious question) Many times one of the utilities has bonded to the original GEC with a split bolt and it was closed up in the wall or ceiling. can't always be sure if something is using it or not. I guess the question really is if there is any harm in leaving it? Hey, what if all the 3 prong receptacles were installed on old 2 wire cable and bonded to that old GEC as it ran past. If you cut it all your Grounds are then NG (we're PG rated here). What do you think? Bill [This message has been edited by Bill Addiss (edited 06-07-2001).]
Bill
|
|
|
|
Anonymous
Unregistered
|
If it is in good shape, I would be strongly inclined to leave it.
If it is deteriorated and I can remove it, I would remove it, just like any other deleted wiring.
If I can't remove it, then I have to bond it.
Leaving it hanging is not an option.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
OP
Member
|
Dspark,
I'm inclined to keep it too if I can't see the full length of it I can't tell if it's being used as a path by other things. I figure that even if it is disconnected or cut from one end (or too short to reach) it is still serving a purpose to 'other' bonded items if any should exist.
Bill
Bill
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
Ok, that's different, the next Q that comes to mind would be how to assess the hidden GEC's usage.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
OP
Member
|
Sparky,
The point is that if it's not detrimental in some way it can be left in place. If it is hidden by finish it might be better left alone, or at least connected at one end.
Bill
Bill
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
ok, in the particular case you pose, it would no longer be a GEC, it would be a 'bond' , or ECG right? so it's connection would follow suit. If the original connection was in question, would you move this to the closest JB ???
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
OP
Member
|
Sparky,
It would be a bond, yes. Do you know of any reason why it shouldn't/couldn't be allowed to remain connected at both ends? That way it would also serve as a redundant/backup GEC?
Bill
Bill
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
Well Bill, I don't see what harm it can do to leave the old GEC connected. I have done many service changes where the meter or the panel are moved.(As i am sure you have also) I have utilized the old GEC and electrodes simply because i beleive more earth contact will achieve the 25 ohms or less ruling, and as you've stated, the possibilty of a backup. GEC's can be installed in singular runs, so by code we could have as many seperate GEC runs as electrodes we desire. If the original GEC has been installed correctly, the only possible parrallel path would be back to the serving utility X-former through common water or other mettalic lines in the event of a noodle faluire ( old ground, i know) The event of a lighting strike or other power surge would, in theory, see ampacity divide among the many GEC's better???
|
|
|
Posts: 349