The Electrical Contractor Network
ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals
Books, Tools and Test Equipment for Electrical and Construction Trades
Live Chat
Join in a Live Electrical Chat!
>> Enter/Register
  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Looking for a unique adjustment nut
by sparkyinak
02/09/12 02:16 AM
A taper or B taper, which is it?
by JoeTestingEngr
02/09/12 12:39 AM
GE low-voltage remote control relay system
by Albert
02/08/12 10:26 PM
Electrical systems in mobile structures.
by gfretwell
02/08/12 09:21 PM
Conduit Bending Apps for iPhone -Master Bender
by KJay
02/08/12 08:31 PM
A What's right here??
Shout Box
Top Posters (30 Days)
gfretwell 72
HotLine1 66
KJay 34
sparky 28
renosteinke 26
Classified Ads:
Electrical-Classifieds.com
Who's Online
0 registered (), 96 Guests and 2 Spiders online.
Topic Options
Rate This Topic
#191253 - 12/22/09 11:34 PM choosing terminal lugs
HongYen Offline
Loc: china
Hi everyone,
I'm trying to choose a suitable terminal lug for my application.
To conduct 550A rms in a 1.06mm diameter wire, it was calculated to require 50mm^2 of wire.
However, when i went to find terminal lugs, AWG 1/0 lugs can only take about 200A.
550A rms is not a continuous working current, but will be reached as certain operation points.
How should i choose terminal lugs for 550A rms please?
Any comments/suggestions appreciated.
Regards,
mactech001
Top
#191266 - 12/23/09 10:13 AM Re: choosing terminal lugs [Re: HongYen]
sabrown Offline
Loc: Ogden, Utah, USA
My answer is based on several assumptions and the National Electrical Code.
Seems to me that you need to go back and check your calculations or I am misunderstanding what you are asking. Without doing calculations on the wire, but looking up 550 amps on the tables, it would require a 1250 kcmil (32.74 mm dia, 633 mm^2) conductor.
A 1.06 mm dia wire is 18 AWG and rated for 14 amps at 90 degrees C, while a 50 mm^2 are cable would be closest to a #1/0 AWG and rated for 150 amps at 75 degrees C.
So are we dealing with a Motor or someother device with an in rush current of 550 amps? It makes a huge difference.
Is this is for a product that is going into production, or a one time sizing? If production you need to talk to someone above you for direction, you may end up with something that is non-listable, but may be a hazard o life and property.
I am making the assumption that you are a young (in the feild, not neccesarily age or time engineering in other areas of the feild) engineer (based on your use of the term RMS), not just someone unconnected with the electrical field. If you are a young engineer, please find a good old salt of the earth licensed electrician (or an electrical engineer in the feild) to work with to help you with all the things they don't teach us in school in this area of the electrical field. Specific education in this area is needed and it helps alot to get out there and get your hands dirty. Also, if you are an engineer stick around and learn. If you are not, you are way in over your head.
I sure hope that the little catch phrases translate well, just seeing that you are from China.
Top