ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 263 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#190394 11/15/09 04:53 PM
Joined: Apr 2007
Posts: 5
T
Terp93 Offline OP
New Member
Hello, I have dryer hookup question. I purchased a new dryer, and I hired an electrician to replace the old 1950’s three wire outlet with a four wire outlet. He recommended not replacing the existing wiring, and that the conduit that runs from the outlet to the panel could be used as the ground, so there was no need to run a separate ground wire.

When he connected the new four wire dryer cord to the appliance, he attached the green ground wire to the metal frame along with the yellow/green wire. Now comes the question, should the yellow green wire be attached to the frame as well, or should it be connected to the Neutral post? There is no ground wire going from the outlet to the panel, so this configuration seems correct. What do you guys think?

Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
SOunds correct to me. Yellow/green is a common identifier for the ground wire, and the whole purpose of the 4-prong receptacle is so that you do NOT connect the ground to the neutral.

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I hope he tested the integrity of that conduit as a grounding path.


Greg Fretwell
Joined: Aug 2006
Posts: 356
Member
Greg,
Integrity of the conduit for an effective ground fault current path has always been my concern. so I always try to install an additional EGC.

How do you test the integrity of the conduit?



Be kind to your neighbor, he knows where you live

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I would use my Ecos tester. That verifies < 1 ohm under a load.


Greg Fretwell
Joined: Apr 2007
Posts: 5
T
Terp93 Offline OP
New Member
Thank you for the help. I’ll ask him if he tested the integrity of that conduit as a grounding path. If the answer is no, I’ll ask him to run an additional EGC to be safe. This site is a great resource.
Thanks again

Joined: Apr 2007
Posts: 5
T
Terp93 Offline OP
New Member
I’m going to add a ground wire, but I have a ground wire size question. The dryer feed is a 10/3. Can I use a 12 wire as a ground, or do I need to use a 10?


Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
How about calling the guy you hired back, and asking him to do it?

Joined: Apr 2007
Posts: 5
T
Terp93 Offline OP
New Member
That sounds like a plan.

Joined: Jun 2004
Posts: 1,273
T
Member
Circuits with OCPD at 30 Amps will require #10 grounding conductors unless the raceway/EMT is suitable.


Tesla
Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5