#190138 11/07/09 02:14 PM
Joined: Mar 2005
Posts: 240
Member
I have an island(slab)with a range in it, I will need to pull thwn through my raceway to feed it, the manufactures specs say it has a maximum amperage of 27.6 amps and requires a 40 amp cord for connection. Can I feed a 40 amp plug with only 30 amps? Seems as an apprentice, my old company got gigged for this exact same thing. What say you?
Thanks,
H20

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
230.23

Quote
(B) 30-Ampere Branch Circuits. A 30-ampere branch circuit shall be permitted to supply fixed lighting units with heavy-duty lampholders in other than a dwelling unit(s) or utilization equipment in any occupancy. A rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating.


Greg Fretwell
Joined: Nov 2007
Posts: 764
K
Member
What I have noticed, over the last several years anyway, is how difficult it is sometimes to decipher range manufactures listed installation instructions and electrical requirements.
Often they list a minimum circuit ampacity as well as a minimum conductor size that doesn’t seem to correspond directly to the nameplate rating of the appliance.

I can remember a couple of years ago with one dual-fuel range, the installation instructions said to install a 30A 4-wire receptacle in the location specified on the template, but when I read the actual electrical requirements in the instructions, they stated to use a #8 minimum conductor size for the branch circuit.

Because of this, I always try and get copies of the manufactures installation instructions whenever I get the appliance schedule for a job.