The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
450.3(C)
by gfretwell
05/22/12 09:32 PM
100AMP panel in 60 degree ambient what size wire?
by mikesh
05/22/12 06:49 PM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
Back to back bends on electric bender
by Tesla
05/20/12 05:38 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 28
HotLine1 27
sparkyinak 17
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
2 registered (twh, gfretwell), 102 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Page 5 of 5 < 1 2 3 4 5
Topic Options
Rate This Topic
#190697 - 11/30/09 08:35 PM Re: Bonding of metal siding [Re: HotLine1]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 4653
Loc: Blue Collar Country
I have no problem with a 'spec' .... and I have a confession to make:

I almost always use the 'quick reply' box. This seems to specifically address my comments to the previous poster ... when that is not always my intent.

In this case, two posters mentioned #6; I thank both of you for responding, and I understand both approaches.

For general discussion purposes, if the intent is to cause a breaker to trip should someone get a shock off the siding, I'm not sure I'd approach the matter the same way. I don't think there's anything in the code that would require a wire larger than #14, I don't think you need to use lugs, and I would want the wire to land on the bussbar in the panel. That's how it looks to me, anyway. I don't see the metal siding as being part of the grounding electrode system at all.

Top
#190698 - 11/30/09 09:14 PM Re: Bonding of metal siding [Re: renosteinke]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Reno:
The siding is NOT any part of the grounding electrode system, the discussion is regarding bonding the siding, or that's what I thought.

Bonding conductors are sized based on the OCP of the circuit that is likely to energize the conductive material. Hence, as I said on page 1, the largest OCP IMHO would be the service main, and in actuality the OCP at the utility primary. With the al. siding 'floating'...it could become energized by a fault, ranging from a 15 amp branch, to the 100+ service main, or the utility primary. Now, bond the al. siding, a fault trips the branch feeder, or...the al. siding vaporizes.

Sticking with a resi job, IMHO other that the service, the largest OCP would likely be the HVAC, or possibly a hot tub at 50 amps, hence a #10, or good old #6 for a 200 amp service.

Again, this scenario is not (to the best of my knowledge) addressed within the NEC directly, but..."likely to become energized" could be interperted many ways.
_________________________
John

Top
#190699 - 11/30/09 09:28 PM Re: Bonding of metal siding [Re: HotLine1]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 4653
Loc: Blue Collar Country
I follow you now. Another poster mentioned running the wire to a ground rod ...