The Electrical Contractor Network
ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals
Books, Tools and Test Equipment for Electrical and Construction Trades
Live Chat
Join in a Live Electrical Chat!
>> Enter/Register
  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Looking for a unique adjustment nut
by HotLine1
Today at 07:14 AM
A taper or B taper, which is it?
by JoeTestingEngr
Today at 12:39 AM
GE low-voltage remote control relay system
by Albert
Yesterday at 10:26 PM
Electrical systems in mobile structures.
by gfretwell
Yesterday at 09:21 PM
Conduit Bending Apps for iPhone -Master Bender
by KJay
Yesterday at 08:31 PM
A What's right here??
Shout Box
Top Posters (30 Days)
gfretwell 72
HotLine1 68
KJay 34
sparky 28
renosteinke 26
Classified Ads:
Electrical-Classifieds.com
Who's Online
1 registered (Albert), 126 Guests and 3 Spiders online.
Page 2 of 2 < 1 2
Topic Options
Rate This Topic
#190051 - 11/04/09 09:44 AM Re: Mini Home Generator System Design [Re: renosteinke]
gfretwell Offline
Loc: Estero,Fl,usa
We are talking about regrounded neutrals here, not mis-wired phases.
Tell me you have never seen a regrounded neutral in a place that has been running trouble free for decades.
Usually these get found when someone adds an AFCI or GFCI
_________________________
Top
#190052 - 11/04/09 11:28 AM Re: Mini Home Generator System Design [Re: gfretwell]
renosteinke Online   shocked
Loc: Blue Collar Country
Greg, my error with that UPS system was related to the neutral hook-up ... not the 'hot' wires. I can't claim to remember the details, and I never did understand the issue - only that the APC tech immediately spotted the problem.
Installing several more similar systems since then, the same little detail always makes me pause. The systems have a few more quirks as well, but that's a topic for another thread.
Top
#190053 - 11/04/09 12:00 PM Re: Mini Home Generator System Design [Re: gfretwell]
SteveFehr Offline
Loc: Chesapeake, VA
Originally Posted By: gfretwell
The generator is not bonded (Honda) but even if it was, the worst thing I can see is you would have some neutral current on the ground. Which wire would burn up?
I have seen plenty of improperly wired SDS transfer switches and no outward problems. As a practical thing it is the same as those 4 wire sub panels with a rebonded neutral.
If your generator has outlets on it, the neutral is bonded to the generator frame. Nearly every small generator in the US is designed like this. Permanantly mounted generators can remove this bond, but it's generally not feasible to remove this bond on portable generators as it would float the neutral in the gen when running stand-alone. Leaving the only proper solution as switching the neutral in the transfer switch.
Top
#190062 - 11/04/09 08:11 PM Re: Mini Home Generator System Design [Re: SteveFehr]
KJay Offline
Loc: MA, USA
The only installation issue I can see is maybe if the subpanel is flush mounted within the wall, since the transfer panels are usually surface mount. Getting that flexible conduit that comes attached to the little transfer panel into the subpanel may require some cutting of the drywall and drilling a stud. No big deal, but still an added pain.
Are you going to use a hard wire transfer panel model with a WP power inlet mounted outside the building or just a long cord and plug connection hookup?
I’m just envisioning the HO dragging a power cord into the laundry room during a power outage.
Top
#190066 - 11/04/09 09:10 PM Re: Mini Home Generator System Design [Re: SteveFehr]
gfretwell Offline
Loc: Estero,Fl,usa
The little Hondas are not bonded
Top
#190067 - 11/04/09 09:45 PM Re: Mini Home Generator System Design [Re: KJay]
wewire2 Offline
Loc: California
The laundry room installation got derailed for exactly the reasons you mentioned. The new plan is to intercept the feeder and put a 125A transfer switch out by the meter. I'll
install a 20A 220V. male twistlock receptacle for the generator input. The meter is in the exterior garage wall
so it will be easy to surface run conduits inside.
Top
#190068 - 11/04/09 10:03 PM Re: Mini Home Generator System Design [Re: wewire2]
wewire2 Offline
Loc: California
Regarding the bonding. I'm planning on leaving the
bond in the main, isolating the solid neutral connection
in the xfer and running a ground wire out for the generator frame to be safe. If a switched neutral is required by code please cite code section.
Top
#190277 - 11/10/09 02:03 AM Re: Mini Home Generator System Design [Re: wewire2]
farmANhvacguy Offline
Loc: wisconsin
Is the 20amp twist the largest outlet? If you have a 30 amp I would use that option
Top
Page 2 of 2 < 1 2
ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals
