#189801 - 10/25/09 09:42 PM
Re: Generator outlet
[Re: Trumpy]
|
New Member
Registered: 11/24/08
Posts: 7
Loc: wisconsin
|
This is a outlet I pulled out of a 28KW winco PTO generator It had no neutral wire just this jumper connecting the neutral to the ground. Seems to me once the plate screw on that outlet got loose it would get a little sparky...........
|
|
Top
|
|
|
|
#189803 - 10/25/09 10:09 PM
Re: Generator outlet
[Re: farmANhvacguy]
|
Member
Registered: 02/06/03
Posts: 932
Loc: Wi/ Paris France { France for ...
|
That what the older generators were used to do that but with current codes etc it no longer legit due the safety issue like what you ran into it.
and in 2011 NEC code cycle everything on generator it will have to be GFCI on 120 volt circuit not sure about 240 volt circuit they may include it or not.
Merci, Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
Top
|
|
|
|
#189856 - 10/28/09 06:33 AM
Re: Generator outlet
[Re: frenchelectrican]
|
Member
Registered: 12/17/01
Posts: 2111
Loc: Vienna, Austria
|
GFI? Doesn't that require a ground reference? All small portable generators here are floating systems without a grounded pole, so all they can do is use protection like in an IT (isolated ground) system.
|
|
Top
|
|
|
|
#189862 - 10/28/09 10:29 AM
Re: Generator outlet
[Re: renosteinke]
|
Member
Registered: 07/20/04
Posts: 7034
Loc: Estero,Fl,usa
|
If the generator isn't grounded somewhere the GFCI will not trip because there is no return path to unbalance the circuit. I know we always say you don't need a ground to trip a GFCI but that is because the utility is a grounded supply.
_________________________
Greg Fretwell
|
|
Top
|
|
|
|
#189873 - 10/28/09 03:34 PM
Re: Generator outlet
[Re: renosteinke]
|
Member
Registered: 01/22/05
Posts: 14
Loc: Miami
|
Pardon me if I don't see the issue here. Are not neutral and ground normally strapped together at the distribution panel? Since the genset is the power source, distribution panel and outlets all in one, wouldn't it make sense to strap them together there? Or should they be strapped together before the run to the outlet? Since the frame of the generator MIGHT be grounded, I would want a nice solid return path in the event that hot shorts to a metal chassis in a tool that I'm using. Better to trip the breaker than have 120V AC finding a convoluted path through my body, into the ground and back to the genset... Correct my amateur self if I'm wrong. 
|
|
Top
|
|
|
|
#189876 - 10/28/09 04:55 PM
Re: Generator outlet
[Re: zorinlynx]
|
Member
Registered: 07/20/04
Posts: 7034
Loc: Estero,Fl,usa
|
We have to separate a generator out in the yard that is not connected to anything but the loads from a generator that is connected to the home wiring, no matter how.
If this is just an unconnected generator, like Reno says, there is no fault path and no shock hazard
_________________________
Greg Fretwell
|
|
Top
|
|
|
|
#189897 - 10/28/09 11:09 PM
Re: Generator outlet
[Re: gfretwell]
|
Member
Registered: 03/29/04
Posts: 199
Loc: Kingwood, TX USA
|
I have a Honda EU2000. Neutral is NOT connected to ground. Case is plastic. Although you could have an internal fault that would cause a ground fault (on ether leg)I like using this unit to power tools and such used in wet or damp locations due to its isolation. I have to admit, this unit is one of the best purchases I have made. Quiet, only 49LB, 12-14 hrs on a tank of gas,very stable voltage and 60 cycle ( 1.1 gal)Beats a 200 ft extension cord.
|
|
Top
|
|
|
|
#189952 - 10/30/09 07:21 PM
Re: Generator outlet
[Re: zorinlynx]
|
Member
Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
|
Pardon me if I don't see the issue here. Are not neutral and ground normally strapped together at the distribution panel? Since the genset is the power source, distribution panel and outlets all in one, wouldn't it make sense to strap them together there? Or should they be strapped together before the run to the outlet? Since the frame of the generator MIGHT be grounded, I would want a nice solid return path in the event that hot shorts to a metal chassis in a tool that I'm using. Better to trip the breaker than have 120V AC finding a convoluted path through my body, into the ground and back to the genset... Correct my amateur self if I'm wrong.  I completely agree, there is no problem here, in fact the neutral MUST be strapped to ground per code, and this is as good a place as any for the manufacturer to do so. Big commercial generators do the exact same thing, just with a larger wire. Of course, modern generators of this sort should be GFCI protected. The GFCI would work just fine even without any solid bonding to ground. If the generator is insulated and there is a ground fault somewhere, no current flows because the "hot" wire is now the only grounded point in the system, and the ground/neutral are now rotating 120V above ground. Of course, it's highly unlikely that the hot will be grounded and ground not intentionally or incidentally grounded at some point. This is why the ground/neutral bond must be made on the line side of the GFCI circuit. If it's a very weak incidental ground, like the grounded gen rails are sitting on a concrete slab, you still might not get the 5ma required to trip the GFCI, but then, if you're not getting 5ma, then it's not really an issue, is it?
|
|
Top
|
|
|
|
#189971 - 10/31/09 08:35 AM
Re: Generator outlet
[Re: SteveFehr]
|
Member
Registered: 12/17/01
Posts: 2111
Loc: Vienna, Austria
|
It is like an IT system - one ground fault and you're fine because you just grounded one leg of the generator like in house wiring. If you get two ground faults then things get nasty.
|
|
Top
|
|
|
|
#190072 - 11/05/09 01:21 AM
Re: Generator outlet
[Re: Texas_Ranger]
|
New Member
Registered: 11/24/08
Posts: 7
Loc: wisconsin
|
So then its ok for 20 amps to flow from neutral thru tab into ground screw into outlet body.........the ONLY connecting to the commen ground/neutral on this generator is the plate screw into the frame... Doesnt seem right to me
|
|
Top
|
|
|
|
#190272 - 11/10/09 01:18 AM
Re: Generator outlet
[Re: renosteinke]
|
New Member
Registered: 11/24/08
Posts: 7
Loc: wisconsin
|
no reno this is my picture there was NO neutral wire..the tab was the "neutral wire"
On the new outlet I ran a wire from the commen ground/neutral block and ran a green wire from the outlet to the generator frame.
this seems a little bit safer to me
Edited by farmANhvacguy (11/10/09 01:20 AM)
|
|
Top
|
|
|
|
#190345 - 11/11/09 10:45 PM
Re: Generator outlet
[Re: noderaser]
|
Member
Registered: 03/29/08
Posts: 127
Loc: Berkley, MA
|
do we have a generator model, i want to go look up a wiring diagram...
_________________________
-Joe “then we'll glue em' then screw em'” -Tom Silva TOH
|
|
Top
|
|
|
|
#190349 - 11/12/09 01:18 AM
Re: Generator outlet
[Re: JoeKP]
|
Member
Registered: 02/06/03
Posts: 932
Loc: Wi/ Paris France { France for ...
|
I am pretty sure the OP mention to me some time back it is a WINCO pto generator I don't recall what KW size it is but I am pretty sure it is 15 KW size but I will let the OP give the correct infomation here. Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
Top
|
|
|
|
#190583 - 11/24/09 08:48 PM
Re: Generator outlet
[Re: WESTUPLACE]
|
Member
Registered: 11/22/09
Posts: 10
Loc: Canada, eh
|
No need for a ground to trip a GFI, as it simply measures the current going thru the hot, and compares to neutral. If they're not the same, GFI trips, aggravates user. XD
|
|