The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Page 2 of 2 < 1 2
Topic Options
Rate This Topic
#189952 - 10/30/09 07:21 PM Re: Generator outlet [Re: zorinlynx]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Originally Posted By: zorinlynx
Pardon me if I don't see the issue here.

Are not neutral and ground normally strapped together at the distribution panel?

Since the genset is the power source, distribution panel and outlets all in one, wouldn't it make sense to strap them together there?

Or should they be strapped together before the run to the outlet?

Since the frame of the generator MIGHT be grounded, I would want a nice solid return path in the event that hot shorts to a metal chassis in a tool that I'm using. Better to trip the breaker than have 120V AC finding a convoluted path through my body, into the ground and back to the genset...

Correct my amateur self if I'm wrong. smile
I completely agree, there is no problem here, in fact the neutral MUST be strapped to ground per code, and this is as good a place as any for the manufacturer to do so. Big commercial generators do the exact same thing, just with a larger wire.

Of course, modern generators of this sort should be GFCI protected. The GFCI would work just fine even without any solid bonding to ground. If the generator is insulated and there is a ground fault somewhere, no current flows because the "hot" wire is now the only grounded point in the system, and the ground/neutral are now rotating 120V above ground. Of course, it's highly unlikely that the hot will be grounded and ground not intentionally or incidentally grounded at some point. This is why the ground/neutral bond must be made on the line side of the GFCI circuit. If it's a very weak incidental ground, like the grounded gen rails are sitting on a concrete slab, you still might not get the 5ma required to trip the GFCI, but then, if you're not getting 5ma, then it's not really an issue, is it?

Top
#189971 - 10/31/09 08:35 AM Re: Generator outlet [Re: SteveFehr]
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2111
Loc: Vienna, Austria
It is like an IT system - one ground fault and you're fine because you just grounded one leg of the generator like in house wiring. If you get two ground faults then things get nasty.

Top
#190072 - 11/05/09 01:21 AM Re: Generator outlet [Re: Texas_Ranger]
farmANhvacguy Offline
New Member

Registered: 11/24/08
Posts: 7
Loc: wisconsin
So then its ok for 20 amps to flow from neutral thru tab into ground screw into outlet body.........the ONLY connecting to the commen ground/neutral on this generator is the plate screw into the frame... Doesnt seem right to me

Top
#190077 - 11/05/09 08:38 AM Re: Generator outlet [Re: farmANhvacguy]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 4607
Loc: Blue Collar Country
I think you have the flow backwards.

There's a neutral wire back to where the generator makes the electricity; what's lacking is the ground wire. So, only current that has energized the frame will use that tab, to return to the system.

Top
#190272 - 11/10/09 01:18 AM Re: Generator outlet [Re: renosteinke]
farmANhvacguy Offline
New Member

Registered: 11/24/08
Posts: 7
Loc: wisconsin
no reno this is my picture there was NO neutral wire..the tab was the "neutral wire"


On the new outlet I ran a wire from the commen ground/neutral block and ran a green wire from the outlet to the generator frame.

this seems a little bit safer to me


Edited by farmANhvacguy (11/10/09 01:20 AM)

Top
#190281 - 11/10/09 09:03 AM Re: Generator outlet [Re: farmANhvacguy]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 4607
Loc: Blue Collar Country
OK, if that's the case, I stand corrected ... and I don't like the design either.

Top
#190344 - 11/11/09 10:27 PM Re: Generator outlet [Re: renosteinke]
noderaser Offline
Member

Registered: 03/01/07
Posts: 401
Loc: Portland, Oregon, United State...
So, there was only a hot connection, and neutral/ground through the generator frame?
_________________________
http://www.hsiprodsvcs.com/

Top
#190345 - 11/11/09 10:45 PM Re: Generator outlet [Re: noderaser]
JoeKP Offline
Member

Registered: 03/29/08
Posts: 127
Loc: Berkley, MA
do we have a generator model, i want to go look up a wiring diagram...
_________________________
-Joe
“then we'll glue em' then screw em'”
-Tom Silva
TOH

Top
#190349 - 11/12/09 01:18 AM Re: Generator outlet [Re: JoeKP]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 932
Loc: Wi/ Paris France { France for ...
I am pretty sure the OP mention to me some time back it is a WINCO pto generator I don't recall what KW size it is but I am pretty sure it is 15 KW size but I will let the OP give the correct infomation here.

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#190583 - 11/24/09 08:48 PM Re: Generator outlet [Re: WESTUPLACE]
Luc Offline
Member

Registered: 11/22/09
Posts: 10
Loc: Canada, eh
No need for a ground to trip a GFI, as it simply measures the current going thru the hot, and compares to neutral. If they're not the same, GFI trips, aggravates user. XD

Top
Page 2 of 2 < 1 2



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals