ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 268 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#189511 10/12/09 06:16 PM
Joined: Oct 2002
Posts: 830
S
Member
I have a job where the neutral and ground must be touching causing the GFI to trip. It's on outside lights. I was going to tie the lights themselves on the line side of the GFI and then tie the outlets on the load side, but if I hook the neutral up on the line side that feeds these lights, it trips the GFI. On the older models I don't think it mattered on the line side. I've taken the lights apart before and didn't see any "shorted out" neutral and
ground, so I'm assuming it's underground somewhere and inaccessible. Anyone ever had a problem similar to this? I guess I'll have to bring another circuit just for the outlets, so the GFI won't trip... Steve..

sparkync #189512 10/12/09 06:46 PM
Joined: Nov 2007
Posts: 764
K
Member
It sounds like if your connecting the grounding conductors together in that box, then that is most likely the problem, since the fault will now be common to the neutrals on both the line and load side of the GFCI receptacle.