http://www.nema.org/stds/fieldreps/codealerts/20090928fl.cfmDoes this mean that 1 & 2 family dwellings don't need GFCI protection on their pools?
Section 2705 Equipotential Bonding GFCI Protection
2705.1 NFPA 70 - 08: National Electric Code, Article 680 (Swimming Pools, Fountains, and Similar Installation), Section 680.22(B), GFCI Protection, is amended to read as follows:
(B) GFCI Protection. Outlets supplying pool pump motors from branch circuits with short-circuit and ground-fault protection rated 15 or 20 amperes, 125 volt or 240 volt, single phase, whether by receptacle or direct connection, shall be provided with ground-fault circuit-interrupter protection for personnel.
Exception: One-and two-family dwellings.