1 members (Scott35), 194 guests, and 11 robots.
wewire2 Offline OP
My supplier cannot find a manufacturer that offers a 200A.
120/240V. meter/main commercial panel with test bypass that is rated over 22 KAIC. Anyone else run into this? Fused panels are available but the client wants breakers.
Y
Whats the impendence of the transformer???
22 k seems up there fer 120/240 volt single phase>??
What K is readly available??
wewire2 Offline OP
22K panels are usually in stock. I am getting the specified AIC ratings off of the engineered drawings or utility reports. Seems like most of the jobs we do are 42-65 K rated.
Y
If impendence is less then Aprox. 2.2 then you gotta jump up to 22000 .
50 kva secondary 208amps.
2.2 at 208 volts single phase. APROX.
I get APROX. 9454 , Its less if a distance away.
Check with Eng. But power companys always go high so do designers. You never wanna be lower then whats really required!!!!
Did you check with Sq.D ?
wewire2 Offline OP
Tried Square D. B-line, Cutler Hammer, Milbank.
RSE Sierra
If they don't have it, they'll manufacture what you need for your specs.... I believe they use Siemens gear
wewire2 Offline OP
I wonder why special order was not offered as an option. I'll have to check that one out. Thanks!