For those wanting to know my preferred method of bringing power to a pole, click on this sketch:

[Linked Image from electrical-photos.com]

Last edited by renosteinke; 09/20/09 05:13 PM.
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Dec 2000
Posts: 4,294
Member
I prefer to keep my "in ground" boxes to a minimum, bringing the conduits directly into the poles.

It's not only more cost effective that way, the connections aren't underground.




Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
I can appreciate the 'clean' results you get, and handholes certainly are expensive (Even a box store version will set you back $30). My way is just the result of too many gnarly repair jobs.

That is, I've had the power run be damaged many times, usually because the feed was simple UF, run just under the sod frown. With the small size of most handholes - and many poles lack even small handholes - making splices in the poles can be a challenge. Of course, if there is no 'sweep' going into the pole, there will be no way to re-pull the wires (either because of a sharp bend under the pole, or because of the concrete around the pole).

Often I'll encounter some attempt to use "Bell boxes" for the connections. I don't like the boxes when mounted on the side of the pole, because of support issues, vulnerability to damage, and difficulty in fishing wire. Placing a "Bell box" either in the ground, or in the concrete, is unsuitable for the same reasons, plus the added issues of corrosion, and the fact they fill with water and muck anyway.

Finally, I've encountered several instances of wires either shorting, or actually breaking, inside poles. Without a pull point nearby, you're in for a nasty job.

Between careless drivers, demented gardeners, and simple bad luck, pole lights are one instance where Murphy was an optomist. laugh

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
Quote
I think that PVC terminal adapter is not listed for the purpose. Matter of fact, I'm surprised that the flex didn't just pull out of the glued fitting before the TA snapped at the pole.
A proper sealtight fitting should be used.


I believe the reason glue on adapters are NOT listed for sealtite is because you can't remove them. I know if you do a good job of gluing them on they won't come off, even with 80 PSI of water pressure and flexing. (RNC, LNFC feeding a hose bib on a floating dock for the U/V protection)
The spa guys use "spa flex" that is basically white sealtite for spa plumbing. They do use primer tho.


Greg Fretwell