235
27
RE potential issue of zip-tying Low Voltage control wire to the power conductor conduit for an AC unit, I take it back.
It appears under NEC2005 section 300.11(2)(B)((2) it is adressed as being OK.
Yet, I still wonder about the control wire being zip-tied to the refrigeration line set as meeting code.
Posts: 9,931 Likes: 34
The general consensus is that it is OK to strap the thermo cable to the refrigerant lines around here, at least that is what I see most of the time. They assemble the whole thing on the ground and fish it through the attic as an assembly.
Offhand, I don't know of any NEC requirement for the Class 2 conductors for the outside unit to be sunlight resistant if exposed, nor I am I aware of a requirement for a wet location listing. Can anyone post a code reference? Would 310.8(D) "Locations exposed to direct sunlight" apply? 310.1 Scope doesn't seem to provide an exclusion for Class 2 or any other type of conductor, it seems to be all inclusive. (NEC2005 reference)
You're right about having a whole separate thread.
300.11(B)(2) doesn't say anything about indoors or outdoors, the practice is permitted in either location if it meets the requirements of this section. Usually, the only place I see class 2 wiring properly secured is when it is tied to the flex at the outside unit, the rest of the cable is just laying on the ceiling panels, draped across trusses, conduits, pipes, etc.
300.11(B)(2) doesn't say anything about indoors or outdoors, the practice is permitted in either location if it meets the requirements of this section. Usually, the only place I see class 2 wiring properly secured is when it is tied to the flex at the outside unit, the rest of the cable is just laying on the ceiling panels, draped across trusses, conduits, pipes, etc. Still wondering, do you think the aspects of 310.8(D) "Locations exposed to direct sunlight" apply to the low voltage control wire strapped to the exterior conduit?
I have looked around and I don't see any thermostat cable around here that isn't "sunlight resistant" but we may have a few guys like George who asked the question years ago. Once it is the consensus of most AHJs, that will be the only thing the supply houses stock.
I have looked around and I don't see any thermostat cable around here that isn't "sunlight resistant" but we may have a few guys like George who asked the question years ago. Once it is the consensus of most AHJs, that will be the only thing the supply houses stock. Yet, around here, more often than not the "Armaflex type" insulation on the suction line is dry rotted and reduced to black dust after not too many years in the sun (insulation more or less missing). I wonder if at some point UV / sun tolerant insulation or insulation covering is a mechanical code issue, or certainly a voluntary material Spec issue? (sorry for the side-track, but it is all one system)
I think that has been addressed here in Florida too. I know they don't seem to use the foam rubber type Armaflex anymore. It is more like the material in a swim noodle and does hold up a lot better. The Armaflex is really just to keep the low side line from sweating in the house anyway from what I hear but it is not my trade either.
Still wondering, do you think the aspects of 310.8(D) "Locations exposed to direct sunlight" apply to the low voltage control wire strapped to the exterior conduit? IMO, since there is no specific requirement for sunlight resistance that applies to low voltage cables, the practice should be allowed. 310 does not apply to low voltage cables, otherwise, the cables would have a lot more info marked on them and we would also know what type of insulation the conductors have.
