450.3(C)
by gfretwell
05/22/12 09:32 PM
100AMP panel in 60 degree ambient what size wire?
by mikesh
05/22/12 06:49 PM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
Back to back bends on electric bender
by Tesla
05/20/12 05:38 PM
An old Amprobe model 550
Shout Box
Top Posters (30 Days)
gfretwell 28
HotLine1 27
sparkyinak 17
twh 15
renosteinke 14
Classified Ads:
Electrical-Classifieds.com
Who's Online
1 registered (gfretwell), 108 Guests and 3 Spiders online.
Page 2 of 2 < 1 2
Topic Options
Rate This Topic
#188253 - 07/27/09 12:04 PM Re: Open Delta Buck-Boost [Re: BigJohn]
JBD Offline
Loc: WI, USA
Treat the secondary of a "buck boost" no different than the secondary of a standard transformer. Make your intial calculations ignoring the fact you will use it as a buck boost. The amount the transformer can carry has to do with the way its low voltage windings are connected.
So a 500VA transformer with a 12/24V secondary wired for 24V has conductors rated to carry 20.83A.
Top
#188264 - 07/27/09 09:00 PM Re: Open Delta Buck-Boost [Re: JBD]
Scott35 Offline
Loc: Anaheim, CA. USA
BigJohn;
Glad that we all were able to assist with the Buck/Boost Transformer sizing criteria.
As JBD described above, to figure the capacity of the Secondary Windings - in Amperes, divide the Transformer's rated Volt-Amps by the Secondary Voltage.
Using JBD's example Transformer above, these are the results:
500 VA Transformer - Secondary = 12/24V
* Secondary setup in Parallel for _12V_:
500 / 12 = 41.67 Amps maximum load Current through Transformer.
* Secondary setup in Series for _24V_:
500 / 24 = 20.84 Amps maximum load Current through Transformer.
Determine the "Per-Line" Amperes, which the Load Device will require, by dividing the Apparent Power (Volt-Amps) by the Voltage; or, if available, just use the nameplate Amperes of the Device.
If there is any doubt per these figures, feel free to reply as necessary! We are all here to assist.
Scott
_________________________
Top
#194259 - 05/19/10 01:52 AM Re: Open Delta Buck-Boost [Re: BigJohn]
Tesla Offline
Loc: Sacramento, CA
BJ...
Wire size, insulation rating, temperature rise...
Coil saturation at 60Hz normally never a concern.
Normally the designer spec'd small gauge high-temp conductors with insulation rated to 150 Centigrade. Even so, there's only so many amperes you can shove through the transformer.
This limit is found when the B-B is trying to bump/buck a lot of current a minimal voltage.
Normally this is no sweat since the typical B-B transform is 277 down to 240 ... or 208 up to 240. You do note that the RATIOS are the SAME. Stacking two such common B-B permits 277 to buck down to 208; which was a proposition on another thread.
Thus you have multiple limits: how much the magnetic circuit can handle and how much the conductors can handle. There are frequency limits, also, but at 60 Hz you not be troubled.