You WILL need screened cable between the output of the VSD and the motor.
I've seen this time and again with RFI problems where the installing sparky just used Romex-type cable, do it once, do it properly.
We have a type of cable over here that is called Varolex, it is made specifically for VSD's, I'm not sure if it is available in the US, but using anything less is rather silly.
With regard to the list of things above, the problems with harmonics, bearing burn, etc, got ironed out a couple of years ago, there were a few VSD manufacturers that nearly got sent to the wall, after these things were picked up.
I mean, a factory that has a heap of these things installed, wants action NOW, not wait until the next best thing comes off the production line.
Thankfully, a lot of motors and VSD's were replaced under warranty ( some were out of it too).
But, if you get a brand-new VSD these days, I seriously doubt that (if installed to the manufacturers specs) you'd have any issues.
One caveat though, these devices are certainly not a plug and play thing, there is usually a pretty thick manual that comes with them, this should be read thoroughly (avoid the usual safety warnings garb at the front).
Most of the VSD faults I have ever been sent to have been caused by either the thing not being installed properly or it had not been set up appropriately for it's application (ie: the settings for start up or ramp-down were too slow or too fast).
Just bear in mind, at the end of the day, even with all that flash control system on the front end, you are still using a motor at the other end, VSD's cannot perform miracles.