0 members (),
1,326
guests, and
8
robots. |
|
Key:
Admin,
Global Mod,
Mod
|
|
|
|
Joined: May 2009
Posts: 20
OP
Member
|
I have an example where an Electrical Contractor wired Modbus and other low voltage comms systems as a "home run" style and then when told the bus portion of the job was an incorrect way to assemble a bus topology, they proceeded to splice the wires back together, solder the splices, and then also add wire nuts to the same splices.
(As an aside, the same contractor also ran the shielded 18-2 wires thru pre-existing conduit and junction boxes which also contained various unrelated line votage circuits).
I'm aware under NEC article 300 there isn't technically a problem as the low volt wire is rated to 300 volts and the maximun applied voltage in the shared conduit is either 120, 240, or 277 depending on the building and example (multiple buildings). I am also aware that under articles 725 and 800 it is pretty clear the wires should not be combined in shared conduit.
It's also pretty clear from a signal noise point of view its just plain wrong. IEEE / TIA and other standards and best practices for insturmentation jobs don't seem like rocket science to me.
I've been studying NEC2005, and apparently NEC2002 may have been in effect at the time of the work. I'm told they are more or less the same in the areas of interest, but I also need to know where they may differ.
In numerous observed examples, the wire nuts fall out when opening the junction boxess for inspection, and in some cases the wire splices were found to be snapped when the wire nut was applied.
Question is, where in the NEC Code should I look to pin down the issues with the solder joints being not code compliant?
Thanks fo the help...
|
|
|
|
|
Joined: Mar 2003
Posts: 849
Member
|
Read 110.14 You well find your answers there. Yoopersup
|
|
|
|
|
Joined: Jul 2004
Posts: 10,048 Likes: 38
Member
|
Solder is fine as long as you make a secure mechanical connection before you solder. ![[Linked Image from gfretwell.com]](http://gfretwell.com/electrical/splices.jpg)
Greg Fretwell
|
|
|
|
|
Joined: May 2009
Posts: 20
OP
Member
|
Thanks guys. I just got back from the local Law Library (my source for reference of these codes, short of buying them).
It appears after reviewing both the 2002NEC and 2005NEC, there is very little to mention about the solder issue except what's mentioned in the above comments RE the "mechnically joined" and being "insulated equivalent to..." criteria. There is no mention of whether a wire nut is or is not considered "identified for the purpose of use" as also mentioned, and I suppose a wire nut counts as insulation referencing 110.14 opening paragraph and section (B) splices.
The section seems to be more concerned with the issues of dissimilar metals such as copper and aluminum, which is understandable given the nature of potential connection failures.
I suppose twisting 18-2 standed wire counts as "mechancially joined" in this context.
Any other ideas or suggestions?
|
|
|
|
|
Joined: Jul 2004
Posts: 10,048 Likes: 38
Member
|
Twisted tight and soldered is fine and a wirenut is adequate insulation so you are good to go. It is a whole lot more than most low voltage guys do. I see twisted and a dab of tape as often as anything (landscape guys), little blue wirenuts if they have them handy (HVAC and gate guys). These days most datacom is on punch blocks of some kind. Nobody solders.
Greg Fretwell
|
|
|
|
|
Joined: Jul 2004
Posts: 787
Member
|
Is using a wirenut on a soldered joint "following manufacture's instructions"?
As an EE, I have had to tell people that tinning stranded wire before putting it into a clamping connector, is wrong because the soldered joint might fracture which will result in a loose connection.
Larry C
|
|
|
|
|
Joined: May 2009
Posts: 20
OP
Member
|
Thanks Larry C, I would tend to agree. Keeping in mind that I'm a facility owner, not a contractor. I'm looking for best practice, not minimal acceptable I do have some broken connections that appear to have been from the twisting of the solder when the wire nut was applied... This is an example of the soldered splice Modbus running in shared raceways with line voltage:
Last edited by BullDog; 05/22/09 05:14 PM.
|
|
|
|
|
Joined: Jul 2004
Posts: 787
Member
|
How about exceeding box fill limits?
Larry C
|
|
|
|
|
Joined: Jul 2002
Posts: 8,450 Likes: 4
Member
|
I wouldn't have thought having the two systems in the one box would be legal?
|
|
|
|
|
Joined: May 2009
Posts: 20
OP
Member
|
Larry C - I'm swinging back and analyzing the box and conduit fill, and quite sure they over did it...
Trumpy - Under articles 725 and 800 I can't see how it meets code. Either.
At present I'm gathering my facts and asking the Engineer / Contractor for an explanation.
In the spirit of fairness, I'm looking for someone to point out something I've missed that makes a difference in the situation.
|
|
|
|
|
Joined: May 2009
Posts: 20
OP
Member
|
Furthering to try and sort this out...
As the Low Voltage rules would or would not apply under 725.x for Class 2 and Class 3 signal wires or 800.x for Communications (all subject to circuit rating determination)...
It appears an exception would be if "Class 1 wiring methods" were employed under 725.25 and subsequent sections.
The question that would arise is under 725.27 (A) calling for 18 AWG and 16 AWG as "shall be permitted" to be used... and under 725.27(B) calling for "shall be suitable for 600 volts"...
Any ideas where shielded 24 AWG twisted pair conductors rated to 300 volts might fit in with the examples above?
|
|
|
|
|
Joined: Mar 2003
Posts: 849
Member
|
Possibly get your answer in 725.26 B(1) (2) (3) Mixing of Voltages .Class 1 & Power supply circuits.
|
|
|
|
|
Joined: Aug 2006
Posts: 25
Member
|
if its high voltage no it violates it if low it might pass ill have to check.....
Luke McCoy The NEC Crazy Boy
|
|
|
|
|
Joined: May 2009
Posts: 20
OP
Member
|
Apparently the crux of the matter is if the Class 2 wires were installed via Class 1 wiring methods, then the conductors can all share the same conduit, boxes, etc. Panel wiring methods come into play also.
The distinction that would apply under Class 1 wiring methods would be the need for 16 or 18 AWG wire and 600 volt insulation.
Therefore I would deduce that 24 AWG CM rated wire with 300 volt insulation would be a "no fly" and the wiring would not meet NEC requirements.
|
|
|
|
|
Joined: Mar 2003
Posts: 849
Member
|
Theres a difference between Class 1,2,3 Circuits . Not just the way there installed. Class 1 725.21(A) Class 2 & 3 725.41 then read 725.26 725.55 2005 NEC
|
|
|
|
|
Joined: May 2009
Posts: 20
OP
Member
|
Yooper,
I know, but / and thanks for helping drive the discussion toward NEC subtle details...
Apparently, by driving a Class 2 classification (in this example) based on the power limited supply that feeds it and the Class 2 devices interconnected by the wiring... It is still OK to use Class 1 wiring methods, in other words upgrade the wiring which would then allow the combined conductors in the same raceway (at least, so I'm told.)
Correcting my original post - the Modbus and Lon bus orange wiring in the photo example are 24 AWG with 300 volt rated (CM on the jacket) insulation with soldered twist splices covered by wire nuts.
Last edited by BullDog; 06/27/09 05:47 PM. Reason: typos
|
|
|
|
|
Joined: Mar 2003
Posts: 849
Member
|
The way I read it the Class has a big part in the two being able to be put together as well as the wiring methods. Now if you changed the power supply from a class 2 or 3 to a one that might be a different story. See 725.52 (A) Exception 2 & fPN below Class 1 rated output of Not more then 30 volts & 1000 volt amps.
Last edited by Yoopersup; 06/27/09 08:57 PM.
|
|
|
Posts: 421
Joined: September 2005
|
|
|
|