I have been working on the recertification of a mobile home. The main Panel is 100 amp but is feed by only #6 teck cable protected at 60 amps at the disconnect. the inspector wants this cable rated for 100 amp saying one day the mobile home park will have to upgrade all services too 100 amp.
my next question is I thought ceiling fans had to be mounted to a box that is suitable for fan mounting. I have no idea if the original box is suitable for fan mounting and have no idea how to put a fan rated box in the ceiling of a mobile home, so we removed the fans and installed key less . the customer asked the inspector about this and inspector said he knew of no rule where a suitable box had to be installed for a fan.
Any ideas would be helpful.
|
|
|
|
Joined: Aug 2007
Posts: 853
Member
|
---"recertification of a mobile home."
I have heard this before. But what exactly does it mean?
Is it a change of tenant? a change of location? or what?
Or an actual Recreational vehicle? We call trailer parks here.. "mobile homes", even though they have not moved in 30 +- years,and are up on blocks.
Last edited by leland; 05/13/09 10:15 PM. Reason: Never mind.
|
|
|
|
Joined: May 2003
Posts: 1,158
OP
Member
|
|
|
|
|
Joined: May 2003
Posts: 1,158
OP
Member
|
BTW these are bakelite ceiling boxes.
|
|
|
|
Joined: Aug 2007
Posts: 853
Member
|
Ok, Now I see. For Re-Sale. Must you also recert existing Homes (permanent dwellings)on a re-sale? Thank you.
|
|
|
|
Joined: May 2003
Posts: 1,158
OP
Member
|
Ok, Now I see. For Re-Sale. Must you also recert existing Homes (permanent dwellings)on a re-sale? Thank you. No but that would be a great idea
|
|
|
|
Joined: Jun 2006
Posts: 613
Member
|
Most modern mobile homes are certified by attaching an approval lable. For a lot of years there was no inspection of mobile homes. the years revealed that some of these mobile homes were not made all that well nor wired to the code. Now any mobile home that does not have a lable needs to be inspected before it can be reconnected and apparently resold too.
|
|
|
|
Joined: May 2003
Posts: 1,158
OP
Member
|
Thanks Mike any comment on the feeder cable having to be sized to the demand load of the mobile
|
|
|
|
Joined: May 2003
Posts: 1,158
OP
Member
|
My issue is that the connection box under the moblie that is part of the park distrubution may not handle #3 for box fill and lugs. This is a very old mobile home park. the connection box is very small.
|
|
|
|
Joined: Aug 2007
Posts: 853
Member
|
So,If I understand correctly.
These are 'Permanent' residences, only in 'mobile homes' that that are not 'mobile' (read North East USA 'Trailer park'). Or 'prefab' homes?
If that is the case, The USA (in general) would displace many many people)
#1 They are set up like condos. No land use. #2 They are typically rentals (low income) and the land lord won't fix anything.
|
|
|
Posts: 1,158