I found the link to the "Stanford Prison Experiment" quite enlightening. Indeed, we have seen a fair amount of strutting about on this very forum, usually by AHJ's who have grown accustomed to being the 'final word' in their town!
Now, for the trailer power ....
First, I am in the States, and have no knowledge of your Canadian rules. I just find this thread timely, as I have just done my first 'upograde' of a camper/RV space to a trailer space.
Anyway, I thought you'd like to see what I did, in the course of my 'reinventing the wheel.'
Here is the panel that feeds the trailer:
You can see the connection box under the trailer. I was surprised to learn that I needed to run pipe, AND have a connection box; every trailer I have worked on has had the cable directly connected to the pedestal. Sometimes this cable has been directly buried; most often, the cable is simply laying on the ground.
The city explained that they didn't want the trailer connection / set-up crew to have to open the panel.
A close-up of the box reveals the "NSI" type connectors I provided for the set-up crew. (For the detail-oriented, the pigtails ended up somewhat loncer after I finished my panel connections):
As for ampacity: I sized my feed to my load calculations. In this instance I calculated 103 amps, so I provided a 125 amp service. Our code specifies 100 amp service to any 'dwelling.'