3 conditions must be complyed with.
But as I read it theres nothing saying that the disconnect at 25 ft has to be in the same room over even same floor , long as conductor distance does not exceed the 25feet.
You guys read it the same??
Yoopers

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
I agree, 25ft of conductor is the only 'physical' limitation.

Joined: Dec 2000
Posts: 4,294
Member

I don't see the possible benefit of having the disconnect in the same room as the tap, or on the same floor.

After all, it won't deenergize the tapped conductors.