Hello there!
I've got a situation here where we are setting a 112.5kva480x 120/208 transformer on the roof of a building.
It will supply power to a 400Amp MCB-type panelboard below roughly 40'of conduit and wire away.
Are we required to have a fused disconnect near the transformer (word has it wthin 25')? Where in the code is this requirement if it exists?
Primary overcurrent protection is a 175amp circuit breaker.
Thanks much for any help

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2003
Posts: 849
Y
Member
240.21
Read which one applys in this section for you.
Also read Table 450.3(B).

Last edited by Yoopersup; 02/15/09 12:44 AM.
Joined: Feb 2009
Posts: 3
R
Rhiney Offline OP
New Member
Thanks much Yoopersup.
That cleared it right up for me . A fused disconnect within 25ft it is .