Electricians revenge
1 members (Scott35), 128 guests, and 12 robots.
Rhiney Offline OP
Hello there!
I've got a situation here where we are setting a 112.5kva480x 120/208 transformer on the roof of a building.
It will supply power to a 400Amp MCB-type panelboard below roughly 40'of conduit and wire away.
Are we required to have a fused disconnect near the transformer (word has it wthin 25')? Where in the code is this requirement if it exists?
Primary overcurrent protection is a 175amp circuit breaker.
Thanks much for any help
Y
Read which one applys in this section for you.
Also read Table 450.3(B).
Rhiney Offline OP
Thanks much Yoopersup.
That cleared it right up for me . A fused disconnect within 25ft it is .