ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 190 guests, and 30 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 4 1 2 3 4
#184066 01/31/09 08:42 PM
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
It seems that all too often I get called by someone who wants a ground for their computer where the house wiring has no ground. They've had the idea that I could just take a separate ground wire to the outside or to the panel.

I thought that was a code violation because it would be creating more than one path to ground, or something like that. The best that I could do, I would tell them, is to install a GFCI for personnel protection (per NEC 406.3(D)(3))and a surge suppressor for equipment protection.

But today I was reading an old article by Rex Caudwell in which he says that "neither a surge arrestor at the panel nor a point-of-use arrester at the appliance will work properly without a high quality grounding system to dissipate the surge."

So I decided to investigate further and found me 250.130(c), in which I was surprised shocked to learn that I can, indeed, run a separate EGC from an ungrounded recept right out to the GE or any point along the GE system.

So am I getting this right? confused And if so, how could I have missed this all these years? blush crazy

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Aug 2007
Posts: 853
L
Member
--So I decided to investigate further and found me 250.130(c), in which I was surprised shocked to learn that I can, indeed, run a separate EGC from an ungrounded recept right out to the GE or any point along the GE system.

So am I getting this right? confused And if so, how could I have missed this all these years? blush crazy--

many miss this,not the preferred practice but compliant.
unless in Massachusetts. Not allowed here.

Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
Wow. Well, I'll be darned.

BTW, would you tell me then, why this is not the "preferred practice"? Is it for the reason I stated? (or tried to state, in a rather bumbling fashion -- something about multiple paths to ground?)

Joined: Aug 2007
Posts: 853
L
Member
Most like to keep all conductors for a ckt together.Or a new ckt for the device.

Electrically it's fine.

Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
Thanks again.

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
The real problem is how you actually connect this. If you read 300.3(A) it says you can't just string THHN back to a ground point. (not a chapter 3 wiring method)
On the other hand I think if it is suitably protected that is better than having ungrounded outlets.
I have heard of running a new grounded circuit in the accessible areas and tapping off that with fished grounding conductors down/up to the ungrounded outlets through the wall where they are somewhat protected.
I would talk to the AHJ and see what they think.

Personally I would just run new cables for grounded outlets in the locations that actually use the ground. (most consumer products have 2 prong plugs anyway)


Greg Fretwell
Joined: Sep 2005
Posts: 99
T
Tripp Offline OP
Member
Okay, Greg. Lts more code to check out. And you're right: the AHJ is a very good idea.

As for "I have heard of running a new grounded circuit in the accessible area and tapping off that with fished grounding conductors...to the ungrounded outlets through the wall where they are somewhat protected" -- if I am able to fish a ground, usually I can fish the entire NM cable (as you suggest in your next paragraph).

"Most consumer products have 2 prong plugs anyway": I am looking at the adapter for this laptop rigth now and it is 3-prong! smile

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
As was pointed out, if your plug has a ground pin, the equipment expects a real ground. You are taking your chances with an adapter. I certainly would not connect an ungrounded PC to a grounded phone line. Your modem becomes the fault path.


Greg Fretwell
Joined: Aug 2007
Posts: 853
L
Member
Originally Posted by gfretwell
The real problem is how you actually connect this. If you read 300.3(A) it says you can't just string THHN back to a ground point. (not a chapter 3 wiring method)

I would talk to the AHJ and see what they think.

Personally I would just run new cables for grounded outlets in the locations that actually use the ground. (most consumer products have 2 prong plugs anyway)


300.3(2) says we can run the bond/ground alone. 300.4, protection must be considered as well.

That's what I meant by 'Preferred' method Tripp.
If you can snake in the ground,(chances are you need to gt all the way back to the panel anyway) A new ckt is just as easy/hard.

Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
I'm sorry, but I was under the impression that stringing in a new ground was a practice no longer allowed. That is, all conductors had to be in the same cable / conduit.

I remeber this being depicted when grounds were introduced, and I have encountered houses built with a separate ground strung along with the 2-wire romex. Yet, I have heard many assertions that you can't do this any more ... nor can you just tie it to any handy piece of plumbing.

I do see the need for a real ground path, though. Electronic appliances often use the ground path ... either to always have power ("instant on," timers, motion sensors, etc.), or in order for the surge suppressor to work.

Page 1 of 4 1 2 3 4

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5