Our new heat pump has a data plate that shows a minimum required current supply of 29.3 amps. The plate also indicates a maximum allowable current protection of 50 amps. I would have to guess that a 30 amp breaker is going to be constantly opening, particularly during startup in hot weather. Is a 40 ampere breaker going to be hassle free or should I just go for the 50 ampere breaker? I've measured the peak/running current of various pumps and such but have never measured a heat pump to get an idea of the loads they present.
Thanks guys and gals!
|
|
|
|
Joined: Jul 2004
Posts: 9,935 Likes: 34
Member
|
I read that as 10ga wire on a 50a breaker.
Greg Fretwell
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
Go ahead, try the 40 amp ... especially if you have good voltage and a short run. "Maximum" means just that; nothing wrong with a smaller breaker.
Ditto for wire size. Run #8 if it makes you feel better.
"Heat pump" is a bit of a misnomer. Think 'air conditioner,' and not 'pump.'
I'd also look to see if the unit has an auxillary heater in it.
|
|
|
|
Joined: Jul 2004
Posts: 9,935 Likes: 34
Member
|
John has a good point on an air handler, heat pump or not. These usually have a bay for strip heat and you have to see which unit, if any is installed. Sometimes the installation instructions are confusing about what the required ampacity might be since they are generic. There is usually a chart that you use with the various strip heaters listed.
Greg Fretwell
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
I've never installed a single heat pump that did not feature a field installed heat element.
You'll need to add its demand to any conductor calculations.
They can be a real pain. Just figuring out what the mechanical contractor actually installed is the trick.
Good Luck.
Tesla
|
|
|
|
Joined: Sep 2004
Posts: 68
Member
|
Heat pumps are just air conditioning equipment that can transfer heat from outside the building to inside and vice-versa. There will be a outside condenser with it's circuit for the compressor load and condenser fan. The inside unit is typically an air handler with an evaporator coil for heating and cooling using the freon gas. The inside air handler will also have a section of strip heaters made out of nichrome wire. These heaters are used to heat the supply air for the building when the heat pump cannot supply enough heat (or if selected on the thermostat). The heaters also assist in defrosting the outside condenser coil during the "reverse cycle", when the heat pump runs both the compressor and the strip heat and spins the electric meter like crazy.
The code does require that the equipment supplier provide labels for both the inside and outside unit, so you can properly wire them.
|
|
|
|
Joined: Apr 2003
Posts: 362
Member
|
If the wire is rated for 50a (as it sounds like it should) than fuse it at 50a.
Ob
Choose your customers, don't let them choose you.
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
There's often some confusion as to what the ampacity of a wire is, or what the overload protection can be.
As an example, let's consider humble #12 copper wire. A look at the ampacity tables might tell us it's rated at 25 amp - but a little star directs us to a place where the code says 'don't go over 20.'
Read further!
That same citation also details ten different situations where the note doesn't apply, and other rules kick in. Tap rules, motors, welders, and air conditioning are among the exceptions, where we are directed, instead, to specific sections of the code.
For example, I've seen welders with duty cycles so low that you could, following the code rules, put a 100 amp breaker on that #12.
HVAC is another such example where 'following the table' isn't as simple as it seems. Sure, the wire hasn't changed ... but the nature of the equipment has changed what the wire is exposed to. Not only do motors require a starting current far higher than their operating current - the situation is made worse in an air conditioner because that compressor is ALWAYS starting up against a full load (the internal pressure doesn't change). So, for that first few seconds, the motor is fighing an uphill battle. In effect, that 1hp motor has to produce six or seven hp just to get running. Once running, the load drops to well under 1hp (in this example).
The effect of this is that, by measuring temperatures, current draw, and voltage drops, the manufacture has demonstrated that his equipment might need a 50 amp breaker -to prevent the start-up load from tripping it needlessly - while a #10 wire stays cool enough that the insulatio is not damaged .... even under the most demanding of conditions.
This leaves the manufacturer with a choice. Does he supply the electrician with abook of engineering data and a code book, letting him figure it all out? Or, does he simply mark the nameplate : Largest breaker 50 amp, smallest wire #10?
This doesn't relieve the sparky of all his responsibility, but it sure helps. Short cycling, long wire runs, low PoCo voltage, conduit fill, etc., can all mitigate against using the smallest possible wire. Likewise, the sparky may find that he can successfully use a smaller breaker on that particular installation, without nuisance tripping at start-up.
Not mentioned in this discussion (so far) is the role of a motor starter in protecting equipment.
We're required to instal a disconnect. The code is silent about using a starter. The unit already contains a contactor - why would one add a starter?
Because a starter is simply a contactor - with overload devices added. These "heaters" are for protecting the motor against long-term operation under excessive load. One can size these overloads very close to the actual operationg current of the unit without fear of nuisance tripping. You might very well have a circuit that is protected by a 50 amp breaker, while the unit itself is protected by 25 amp overloads.
|
|
|
Posts: 99