Electricians revenge
0 members (), 30 guests, and 10 robots.
#181853 11/03/08 11:23 PM
Erick Offline OP
Guy's I am a crazy with embarrassment but here goes: An electric heater is rated for 2400 watts at 240 volts. What power is consumed when the heater is operated at 120 volts? I=P/E, R=E/I, I=E/R, P=EI, I know the steps but with unequal voltages?? man I am so stumped, I know the answer it's (600) but don't know the formula Ohms law out the window to a point what am I missing?
Erick #181854 11/04/08 12:17 AM
Watts = Amps times Volts
Volts = Amps times Ohms
therefore .. Watts = Amps times amps times Ohms
so ... amps times amps is a 'squared' relationship
that is, reducing the volts by half, and you cut the amps by four (2x2). Thus, 1/4th the heat.
Erick #181855 11/04/08 12:22 AM
First, use this formula to calculate the resistance @ 240 Volts
p = e^2.......p = watts e = volts r = ohms(resistance)
.....R
2400 = (240)^2
...........R
R = ((240) x (240))
.....2400
R = 24 ohms
Then use the same formula to calculate the power at 120 volts:
p = (120)^2
.....24
p = 600 watts
Here are some more formulas that are helpful:
http://www.the12volt.com/ohm/ohmslaw.asp#pie
canuck #181856 11/04/08 01:32 AM
Erick Offline OP
Thanks very much you guy's are great! Erick
Erick #181858 11/04/08 02:13 AM
However, remember that the resistance of the heating element is likely to change with temperature, so 600W is only an approximation.
