The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
100AMP panel in 60 degree ambient what size wire?
by mikesh
05/22/12 06:49 PM
450.3(C)
by Steve T
05/22/12 05:41 PM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
Back to back bends on electric bender
by Tesla
05/20/12 05:38 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 28
HotLine1 28
sparkyinak 17
renosteinke 15
twh 15
Classified Ads:


Electrical-Classifieds.com

Who's Online
1 registered (mikesh), 115 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#181554 - 10/15/08 08:54 PM Collector Bus sizing Problem
theseus Offline
Member

Registered: 02/23/08
Posts: 11
Loc: china
How to size the Collector Bus?
I have 3 1600kw/400V gengerators Synchronized and connected to the Collector Bus.

Top
#181567 - 10/16/08 09:52 AM Re: Collector Bus sizing Problem [Re: theseus]
mikesh Online   content
Member

Registered: 06/07/06
Posts: 567
Loc: Victoria, BC, Canada
Ok I'll bite, (1600 X 125%) + 1600 + 1600 = 5200 amps.
28-108 of the Canadian Electrical code for conductor sizing for Motors.

Method 2 take the connected load at 125% and size the bus for that.

I don't know what a collector bus is but i guessed it is the bus after the transfer switches where each generator parallels.

Top
#181585 - 10/16/08 10:50 PM Re: Collector Bus sizing Problem [Re: mikesh]
theseus Offline
Member

Registered: 02/23/08
Posts: 11
Loc: china
Yes,Collector bus = paralleling bus.

But,generator is different from motor.

Top
#181620 - 10/20/08 10:46 AM Re: Collector Bus sizing Problem [Re: theseus]
mikesh Online   content
Member

Registered: 06/07/06
Posts: 567
Loc: Victoria, BC, Canada
Yes a generator and a motor are not the same but the wires are sized the same. At least that is what i derive from section 28 of the CEC %125 of the first (largest) generator and 100% of the next 2. Generators and motors are very similar in terms of what happens inside them whether making or using electricity. Cooling, winding and loading all apply the same. A stator for a motor and a generator look the same from a winders perspective at least from 28 year old memories they do. I have rewound stators for both. The armatures are different as there is excitation and magnetic fields to build.