ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 260 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#181358 10/05/08 01:14 PM
Joined: Apr 2002
Posts: 197
T
triple Offline OP
Member
I'm hooking-up blowers in some paint booths. These are unsealed, relatively thin steel boxes with bolted together sides. There is a 1/2 hp, 120V, thermally protected motor in each of the four units (per booth). The installation instructions call for the sides/covers to be caulked as they are assembled.

I have two questions. First of all, how can these blower motors be installed in a hazardous location. The construction of the blower box is essentially like using a standard 8x8 steel junction box to house a potential spark producing device inside a hazardous location. Even if I caulked the cover shut, I couldn't get away with such an installation. Also, the multiple caulked covers that would need to be removed to access the motors for service does not seem right to me.

My second question concerns the pipe I need to use to feed these units. The blower housings are not made to have a pipe mounted to them. Instead, 2" holes are provided in the backs to run a flexible pipe through and to the motor. I am going to run a pipe down from the booth ceiling and into the top of the boxes. Six inches of this pipe will be exposed inside the paint booth. There will not be any exposed connectors or couplings and the pipe will be caulked where it enters the booth and where it goes through the caulked-on thin steel top of the blower housing. Once inside, the conduit will be converted to flex and run into the motor.

I am assuming that no disconnect will be needed at the motor since it is inside a hazardous location. However, does the exposed, short, unspliced conduit I use have to be rigid inside the booth and sealed off as soon as it passes through the booth ceiling. Normally, I would be very confident that it would but the apparently "legal" -but flimsy- construction of the blower boxes have me confused.

Any thoughts?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

triple #181363 10/05/08 07:07 PM
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
First....plans & specs??
Second...permit??

My thoughts? I would not touch a job that you describe. Chapter 5 locations demand safe, compliant installations, of SAFE, LISTED/LABELED equipment, not 'whatever looks like it will work'.




John
HotLine1 #181367 10/05/08 08:34 PM
Joined: Apr 2002
Posts: 197
T
triple Offline OP
Member
I guess I should have mentioned that these blowers are designed for paint booths and have some sort of listing for that purpose. I can only imagine that either somebody got paid off big time to allow such a thing or that I completely misunderstand this type of hazardous location. Even though I would normally never imagine doing such a thing, my plan is to use no seal-offs or rigid pipe. It makes no sence what-so-ever with the half-azz box I am running to.

triple #181368 10/05/08 08:50 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
The crux of any classified location is the actual classification of the specific area, and its' boundaries.

Most paint booths are designed to -technically, at least- place the lights and fans outside of the classified zone.

Keep in mind the very big difference in classification of the zone, between "always exposed to hazardous atmospheres" and "only exposed if something breaks." In most instances,TEFC motors, with the starters mounted well away, meet the qualifications. Nor do junction boxes, etc., need to be rated 'explosion proof' if they are in a 'zone 2', are gasketed, and contain no sparking contacts. (Keep THAT detail in mind when mounting your disconnects!)

Oddly enough, your greatest concern is in the grounding of the fans; moving air can create static electricity.