1 members (Scott35), 536 guests, and 30 robots.
#181087 09/22/08 01:44 PM
O
Oh Well Offline OP
Is it acceptable in Canada to make joints using wire connectors in a beaker panel? Thanks in advance
Yes
Can you give a rule number for this?
Sixer
Sixer #181171 09/24/08 12:16 PM
6-212 says no but 12-3032 says you may on a retrofit up to %75 of the area.
So what applies? You can't splice in the service according to 6-212 but can if you are adding to an existing installation? Either way you can't do it in a new installation. Have both rules at hand when you speak to the inspector.
From this jurisdiction we would not allow splices in the service entry section of a combination panel or switch.
