ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 250 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#180967 09/17/08 09:58 PM
Joined: Nov 2005
Posts: 187
HCE727 Offline OP
Member
Years back I installed a GFI outlet in a bedroom that was wired in K&T. Every time I turned on the hallway 3-way, the GFI tripped. Has anyone ever had a problem with GFI's and K & T? After that I now install non-gounding outlets on K & T.


Hank
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I bet you have a short to ground on a neutral. That could have gone on unnoticed forever. It could also be high resistance ground on a hot (petrified mouse or something.


Greg Fretwell
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
I put gfi protection on K&T fairly often.

Joined: Oct 2006
Posts: 745
E
Member
My guess would be that the far end of that three-way circuit (light fixture) is getting it's neutral from something other than the GFI's LOAD neutral output.

Basically, your hot LOAD output is feeding the point wire of the 3-way switch at one end, and the point wire at the other end is feeding the fixture. Problem is that the fixture is getting it's neutral elsewhere, even if it is on the same circuit ahead of the GFI.

Do you need to have the GFI protecting the circuit downstream form the device itself? It's a bit odd for K&T circuits to loop from device to device, but this does happen. Why not just put the in and out wiring on just the LINE terminals and be done with it?


---Ed---

"But the guy at Home Depot said it would work."
Joined: Nov 2005
Posts: 187
HCE727 Offline OP
Member
This happened to me years ago. There was only one hot and one neutral in the box that I installed the GFI in.