I have a concrete plant with 120volt e-stops on it, installed on hoffman metal boxes osha came out and asked if they where less than 50 volts to the e-stops do the e-stops have to be less then 50 volts. This plant was installed in the early 90's and inspected I never heard of this before.

Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
It would not be out of line for you to ask for a specific code reference.

Joined: Dec 2001
Posts: 300
M
Member
OSHA always provides a specific list of violations. They don't just ask about whether something is under 50 volts. They either cite a violation or not. If they didn't, it's fine. If they did, you'll get a notice in the mail within a couple of weeks with everything spelled out.

To answer your question, OSHA considers anything under 50V to be non-hazardous. So if there are exposed energized parts or fuses that need to be changed hot or even light bulbs that need to be changed hot, or something that's not grounded, it's okay under 50 volts but not okay at 50V or more. That's the only 50V distinction I know of.

Joined: Jun 2007
Posts: 301
J
Member
Get a code reference, as to why it is a violation. 120 volt controls are not a violation. Is it possible the E-Stops are in a classified location. I am certain that dust is an issue in concrete plants. Very well could be considered a classified location. But even in a classified location the enclosure would be the protecting means not the voltage.

Joined: Nov 2000
Posts: 2,148
R
Member
A classified location involves flammable dusts, and concrete dust would not result in a classified location.


Don(resqcapt19)
Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
I think ... and this is just a wild guess .... that the inspector was responding to the WET nature of parts of a cement plant, and the need for GFI protection in such areas.

He certainly failed to explain himself ... and you have every reason to ask for such an explanation from him.