0 members (),
516
guests, and
17
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
OP
Member
|
This came up over at Bryan's house and I thought it might spark some interest here. Why are some things considered needing full working space, yet a very similar piece of equipment somewhere else doesn't. Example. A/C condenser disconnects vs water heater disconnects or even the disconnect for the A/C air handler.
Greg Fretwell
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
Very good point. It's often the same exact disconnect.
|
|
|
|
Joined: Mar 2005
Posts: 399
Member
|
The rule is the same. The problem is that the electrician puts the disconnect outside and has it inspected. Then the AC guy comes along and puts his equipment in front of it. It happens in factories all the time especially with air compressors and other machinery. It ends up as an electrical violation even though the equipment installer created the violation. Usually this is done after the electrical inspection. So should the inspector penalize the electrician for some other guys mess ?
Alan-- If it was easy, anyone could do it.
|
|
|
|
Joined: Oct 2006
Posts: 745
Member
|
I've had that happen a few times with hot tub disconnects lately too. You estimate where the edge of the tub will be and plan accordingly, then the customer changes their plan for the yard. Guess what ends up having to be moved? I assure you that it's NOT the hot tub.
It's not the money part; they have been more than willing to pay. It's just that it's sometimes a terrible waste since in at least two instances, the PVC and wire ended up being 20 feet too short. Sure, I got to keep the wire and got paid to replace it, but it's still frustrating.
Same thing happened with a 100 amp furnace disconnect recently when a guy was finishing his basement. The new wall reduced the clearance to 2'-4", more than enough for most people to use. No dice. We had to move it. Again, more money for me, but seemingly senseless.
Excellent subject, by the way.
---Ed---
"But the guy at Home Depot said it would work."
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Alan: re: "It ends up as an electrical violation even though the equipment installer created the violation. Usually this is done after the electrical inspection."
I have to ask, how could the inspection be made without the equipment 'in-place'??
Example: New resi, no HVAC cu's installed, no final inspection! I need the nameplate data to determine correct OCP and conductor sizing.
Yes, the EC takes a few 'shots' from other trades. Communications lacking between the trades; horray for me & tough for you attitudes, poor supervision by the GC/job super/builder.
Poor communications, or worse none at all can lead to expensive rework. That's another thread.
John
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
OP
Member
|
I guess most of you don't have air handlers in closets or in attics. That is the biggest violations I see (ignored). Water heaters would be a close second. How many people have an extra 30" of wall space in a utility room? How long do you think it remains "extra".
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Greg: Usually, as soon as the ink on the CO is dry!
Utility closets/rooms; 'electric/phone' rooms turn into catch-alls probably as soon as I walk down the hall. Maintenance issues are handled (commercial) by the uniformed Fire Dept Inspectors, and it's there cash cow.
Attics, yes & crawl spaces too.
John
|
|
|
|
Joined: Mar 2005
Posts: 399
Member
|
Hot line, I only inspect electrical, Building, Plumbing & Mech are all done seperately. On a new house, January with a foot of snow on the ground the electrician wants his final. He has a disconnect outside to an Air Cond. that will be installed in the spring. Breaker sized for the wire, may have to be adjusted for the equipment. He gets his final, and he gets paid. In the spring the AC gets installed and the Mech inspector does his final, including OC size and if fuses only, etc.
Alan-- If it was easy, anyone could do it.
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
OP
Member
|
I kicked another tar baby over at Bryans house. I asked, why do we really believe the condenser disconnect has to be worked on hot? Isn't this just a safety device for the HVAC tech and all his work should be able to be done in his box, only using the disconnect to disconnect. If he really thinks it is bad (no power on the load end of the whip) why isn't he calling an electrician? Since he should be checking the branch circuit breaker anyway, why not turn it off before he looks in side the disconnect if he must. Why IS this any different than the receptacle behind the fridge? Does the appliance repairman tear into that if he has no power at the face of the receptacle?
Greg Fretwell
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Along those same lines- How much working space is required in front of an alarm panel? Code reference please.
George Little
|
|
|
Posts: 75
Joined: June 2012
|
|
|
|