F
frankgi Offline OP
I recently failed an inspection because the existing exit/emergency lights were on a dedicated circuit with a sp breaker lock. I was told that circuit needed to be tied in with a breaker that controls a row of lights in the vicinity of 2 emergency lights.(There are other e/e's throughout the building....a liquor store) Customer turns the fixtures on and off by the breakers. Just wondering if Art#700.12(F):exception would apply? Light fixtures and e/e's originate from the same panelboard. There are more than 3 rows of lights. My remedy was to tie e/e circuit in with a row of lights to be left on 24/7.
Any thoughts?
Thanks!
"Its all about the small details"
OK, a plain english explanation....
One open large area/room/store/office, etc.
IF three (3) or more lighting circuits in that 'room', you are allowed to have a 'dedicated' exit/em circ w/cb lock.
IF NOT, the exit/em lighting has to be circuited (connected) to the local lighting circuit, before any switch.
You also mentioned 'existing'; did you touch, modify, relocate, or not touch it?
Usually, a retail store falls under the 'more than three (3) circuits', and has a dedicated exit/em circuit with the 'nite lites'. The number of 'rows' is not really relevant, it's the # of lighting circuits.
What part of NJ are you in ?? And what Article was cited? and by who, Elec, Fire or Bldg?
F
frankgi Offline OP
Hi and thanks for your reply.
Just added 1 exit/em with a dual remote head outside, from existing exit/em dedicated circuit. Easily more than 10 lighting circuits from panel. (1 circuit per row)
>What part of NJ are you in ?? And what Article was cited? >and by who, Elec, Fire or Bldg?
SJ.... Art 700 .....Elect
FrankG
Best solution...call and speak to the elec inspector, explain that there are more than 3 circuits, the e/e is dedicated, and there is a breaker lock. Conformance with Art 700 IMHO, from your explanation.
F
frankgi Offline OP
Thanks John.