The lesson is in the struggle, not the victory.
Is this in one of those pain in the neck metal sun rooms? I just had to wire one.
Nope, just plain ol drywall in a living room of an apartmrnt.
Posts: 794 Likes: 3
"But this solved that tripping breaker problem"...
Posts: 9,928 Likes: 34
It all depends, is that a sheet metal screw? You need to bond drywall with a drywall screw.
It all depends, is that a sheet metal screw? You need to bond drywall with a drywall screw. and you must keep the drywall moist
Sixer
Steel studs maybe? this might be up there with the ground clamp on PVC water pipe
It's only approved if you use a machine screw...
What are we looking at here? Is that a heater or A/C unit with the cover removed?
It looks like a3-wire supply cord. Is that green wire just the EGC from the cord, or is it secured to the appliance frame?
It's an A/C unit in an apartment, this wire comes directly from the cord.