Thur experience for Cost (Material & Labor) what have you found to be the most cost effective combination of pipe & wire??? Pvc Sch. 40 with Alum or Copper . I;m looking for 3000 amps. Another words 500 mcm , 750, 1000 copper or alum.
4 wires in a conduit. Useing 310.16 75C & 110.14c for terms.
Yoopers
Also mostly 480 volt loads so Neutral can be 12 1/2 percent of phase conductors right.
Top
Featured Tools
#177423 - 05/02/08 08:19 AM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: Yoopersup]
electure Moderator Offline
Moderator
Member
Registered: 12/24/00
Posts: 3680
Loc: Fullerton, CA USA
Didn't you already ask this question back in February?
Top
#177431 - 05/02/08 11:09 AM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: electure]
resqcapt19 Moderator Offline
Moderator
Registered: 11/10/00
Posts: 2165
Loc: IL
I'd take a look at bus duct for that size feeder.
_________________________
Don(resqcapt19)
Top
#177438 - 05/02/08 03:56 PM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: resqcapt19]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 453
Loc: Michigan
One I posted in Feb was a bit different , Just wondering thur experience which way worked out better.never to proud to learn. Right
Top
#177523 - 05/05/08 06:02 PM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: Yoopersup]
Tesla Offline
Member
Registered: 06/16/04
Posts: 259
Loc: Sacramento, CA
At 3000 Amps your 'window' becomes restrictive, you'll need to stuff 400 Amps in each of eight pipes. That means that you might be forced to go with copper in schedule 40 PVC.

By comparison, bus duct can be had at 3000 Amps in AL.

The shorter path and cheaper conductor makes bus duct a serious competitor.
_________________________
Tesla
Top
#177525 - 05/05/08 06:59 PM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: Tesla]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 310
Loc: Chicago Illinois USA
Another consideration with bus duct is the difference in labor hours. Slap up 1 10' length of bus duct and you're done with 10' of feed. For 10' of conduit you still have to pull and terminate the wires...PLUS you have multiple sets of everything.
_________________________
Ghost307
Top
#177571 - 05/07/08 06:01 PM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: ghost307]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 453
Loc: Michigan
Cost of Buss Duct custom made otta this world .
Top
#177583 - 05/07/08 09:35 PM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: Yoopersup]
George Little Offline
Member
Registered: 01/18/04
Posts: 1197
Loc: Michigan USA
Ernie- You've left out some details (as usual) and I wonder if the question factors in the grounding conductor? With metal raceway - no ground wire- with non-metallic you will need a ground wire- since this is not service. Right? Wrong?
_________________________
George Little
Top
#177590 - 05/08/08 05:17 AM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: George Little]
resqcapt19 Moderator Offline
Moderator
Registered: 11/10/00
Posts: 2165
Loc: IL
How long is the total run? You have to watch out for the length difference with parallel runs.
_________________________
Don(resqcapt19)
Top
#177594 - 05/08/08 06:52 AM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: resqcapt19]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 453
Loc: Michigan
George
Service conduits from utility Co, transformer to Service gear that means NO GROUND WIRE.
Total run is Aprox. 40feet and yes I know about requrements of Parrell runs.
Buss 90's if you've ever installed then cost a bundle as well as regular buss. But I agree worth a price compaireson.


Edited by Yoopersup (05/08/08 06:59 AM)
Top
Page 1 of 2 1 2 >


Featured:

2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides
2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides


Tools for Electricians
Tools for Electricians

 * * * * * * * * Licensing Info and Lookup
Licensing Info
& Lookup

 

Recent Posts
Required Sign Circuits
by HotLine1
01/07/09 08:15 PM
Theater Electric
by HotLine1
01/07/09 08:02 PM
California referal fee legal question
by bwise121
01/07/09 07:59 PM
800 amp transfer switch
by HotLine1
01/07/09 07:39 PM
VFD BURNING OUT MOTOR BEARING
by GETELECTRIC
01/07/09 03:02 PM
Top Posters (30 Days)
renosteinke 49
Trumpy 48
gfretwell 46
HotLine1 41
pdh 31
January
Su M Tu W Th F Sa
1 2 3
4 5 6 7 8 9 10
11 12 13 14 15 16 17
18 19 20 21 22 23 24
25 26 27 28 29 30 31

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals