#177290 - 04/28/08 07:40 AM And yet another Sub question
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 179
Loc: nc
I`m working with a new contractor whom insist I put a main in the house. I have a 200a meter main out side and have installed a 100 main lug inside with the 100 ocp out in the metermain.Guess I`m not going to find in exact words this is legal I showed him I had ocp for the panel to protect everything has someone got some Code references I can shoot at him.
Wouldn`t 408.36 cover it?
Top
Featured Tools
#177294 - 04/28/08 08:11 AM Re: And yet another Sub question [Re: Reel-Break]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 505
Loc: Alaska
I am not sure what you are shooting at with 408.36. The main is the panel is not required per NEC. I doubt that it is a local ordinance since you are saying it is not required. If the contractor or the customer is going to pay for it, give them what they want. It may just give them a piece of mind. If you have already ordered parts, tell them how much it is going to cost for the change. Check you project specs. if the project came with them.
_________________________
"Good judgment comes from experience. Experience comes from bad judgment."
Top
#177298 - 04/28/08 10:05 AM Re: And yet another Sub question [Re: sparkyinak]
BPHgravity Offline
Member
Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
Yes, 408.36 is the correct section to cite in regard to NOT requiring a "main" breaker inside a panelboard supplied by a feeder with proper overcurrent protection.
_________________________
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Top
#177328 - 04/29/08 09:48 AM Re: And yet another Sub question [Re: BPHgravity]
JValdes Offline
Member
Registered: 06/03/07
Posts: 243
Loc: South Carolina
Glad I looked at this thread. I have always understood that a sub panel in an unattached structure requires a main breaker and one or more electrodes, in addition to the main breaker for the feeders.
Is this thread concerning a main service and that is why I do not understand using a lug panel is a violation?
Thanks....john
Top
#177329 - 04/29/08 09:58 AM Re: And yet another Sub question [Re: JValdes]
gfretwell Moderator Offline
Member
Registered: 07/20/04
Posts: 4212
Loc: Estero,Fl,usa
If you go to a second building you need another disconnect but I understand this as all being in or on the same building. This is not that unusual on a piling house where they have a service disconnect at ground level and a lighting and appliance board up in the dwelling.
_________________________
Greg Fretwell
Top
#177332 - 04/29/08 10:26 AM Re: And yet another Sub question [Re: JValdes]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 979
Loc: Chesapeake, VA
In this case, he's got the OCP/service disconnect as a separate breaker, and so does not need a main breaker on his panel.
Top
#177433 - 05/02/08 01:31 PM Re: And yet another Sub question [Re: SteveFehr]
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 179
Loc: nc
Yes this is correct. Small cracker box house just set metermain outside to catch the heat and hvac 100 amp sub 20 space in the house. But the main reason for the metermain is the fact of where the panel was located and poco entrance.I coundn`t go back to back.
Top


Featured:

2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides
2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides


Tools for Electricians
Tools for Electricians

 * * * * * * * * Licensing Info and Lookup
Licensing Info
& Lookup

 

Recent Posts
VFD BURNING OUT MOTOR BEARING
by GETELECTRIC
Today at 03:02 PM
Sizeing a whole house generator
by EV607797
Today at 02:18 PM
Ballast voltage re-configure?
by gfretwell
Today at 02:04 PM
Theater Electric
by ghost307
Today at 01:46 PM
Required Sign Circuits
by pdh
Today at 12:26 PM
Top Posters (30 Days)
renosteinke 48
Trumpy 48
gfretwell 46
HotLine1 40
pdh 31
January
Su M Tu W Th F Sa
1 2 3
4 5 6 7 8 9 10
11 12 13 14 15 16 17
18 19 20 21 22 23 24
25 26 27 28 29 30 31

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals